I have to replace a Lauer PSC090m HMI. It is a PCS090-Plus and the 'm' is for Siemens MPI communications.
I have PCSPro and the PCS733 cable and was lucky enough to find one of these on eBay that works. I have one other line here with the same model that is working. I have the OEM project to transfer into the new one and would like to upload and archive the project out of the running one.
The manual says that to get into transfer mode pin 4 of the programming DB-9 port must be high, and DIL switch 9 must be on for writing. I also found an old thread about these that said PCSPro will not work with USB-serial adapters, so I am trying to connect on a desktop with a serial port on a portable desk.
I can not get either of these in transfer mode - they do not have the DIL switches on the back that the manual shows for the -090.
Does anyone know how to get these into transfer mode without the switches on the back?
I don't want to open either of them to see if the switches are inside - the new one has a warranty sticker and the other the line is running and can't be removed unless i want to come in on Sunday.
I have PCSPro and the PCS733 cable and was lucky enough to find one of these on eBay that works. I have one other line here with the same model that is working. I have the OEM project to transfer into the new one and would like to upload and archive the project out of the running one.
The manual says that to get into transfer mode pin 4 of the programming DB-9 port must be high, and DIL switch 9 must be on for writing. I also found an old thread about these that said PCSPro will not work with USB-serial adapters, so I am trying to connect on a desktop with a serial port on a portable desk.
I can not get either of these in transfer mode - they do not have the DIL switches on the back that the manual shows for the -090.
Does anyone know how to get these into transfer mode without the switches on the back?
I don't want to open either of them to see if the switches are inside - the new one has a warranty sticker and the other the line is running and can't be removed unless i want to come in on Sunday.