level switch potiential free contact
Charbel
Jan 2012
Beirut
307
dear,
i was looking at the datasheet for rotary paddle limit switch, it says that the switch output is potential free changeover contact (SPDT) with connectable load of 3A for the motor which is to be connected to it. it is better to use a contactor.
i was looking at the below link
http://www.finglai.com/product/contactor/AC-contactor/LC1-D09.html
somebody help wiht hte selection of the contactor? considering that the motor rating is 1.5KW.
thank you!
charbel
You did not mention the motor voltage, but the LC1-D09 will be OK.
You just have to select the coil voltage for your project.
What is your control voltage.
If this is a stand alone unit then checkout
Schneider electric
http://www.schneider-electric.com.a.../en/local/automation_and_control/tesys_le.xml
these may work out cheaper - You need to specify voltage and Overload size.
your paddle replaces the start/stop circuit.
the website and part number you quoted is selling Schneider
sorry I forgot
the reason I highlighted the AC3 AC4 rating
this is the number of operations the contactor see's
Rule of thumb
AC3 on an off a few times an hour or day.
AC4 Plugging - on and off constantly
this is how you know if the contactor won't fail
Hello everyone Iam working on washing machine which washing onion and water level is very critical for the process. The machine used IFM 121 for...
144
dear, i am assigning start/stop levels for the sump pump, i was wondering what is the minimum differential level that can be used when a float...
2,603
Dear all, i have LS1200 murphy used for suction scrubber (connected NC contacts to 1756-IQ16 card) and the question is: when i triggered switch...
1,742
Hi Guys, I wrote a Program on Tank Over fill Protection system. There are Five Tanks/Five Rosemount 2120 Level switch inputs and One Audio...
1,588
Dear, I am trying to size level switch contact rating for a specific application. we will be using multilin 469 as below...
1,897