It isn't clear to me what logic interlocks which other logic (MultiLin and pump-down level switch logic), but the level switch animation shows the level switches FST and FSB driving MS1 a motor starter contactor.

That pump-down circuit depends on a latching output from MS1, so if you don't drive a contactor directly with the FSB/FST contacts, you'll need an equivalent latching contact from a relay or from the MultiLin device to achieve the pump down action shown in the animated graphic.

For sizing, it depends on what the level switches 'drive'. A digital input to the MultiLin, or a motor starter, or a relay used for latching.
 
It isn't clear to me what logic interlocks which other logic (MultiLin and pump-down level switch logic), but the level switch animation shows the level switches FST and FSB driving MS1 a motor starter contactor.

That pump-down circuit depends on a latching output from MS1, so if you don't drive a contactor directly with the FSB/FST contacts, you'll need an equivalent latching contact from a relay or from the MultiLin device to achieve the pump down action shown in the animated graphic.

For sizing, it depends on what the level switches 'drive'. A digital input to the MultiLin, or a motor starter, or a relay used for latching.

dear, thank you for your quick reply,

actually if it will be driven by the digital inputs, it will not be more than 20mA as indicated in the datasheets (please refer to attachment)

but I would expect more if it will be driven from the contactor of a 20KW motor, what do you think, it will be in order of 1A or more?

thanks a lot!!

digital inputs of 469.PNG
 
Hi I would take it into a relay and use the relay contacts to do the work. A 4 pole 10A relay is cheap and easily replacable
 
In general a dry contact to the Multilin input will be fine, and there is no concern about amp ratings. If the level switch is in a raw sewage wet well you would be well advised to use an intrinsic safety relay between the switch and the Multilin. This assumes you are using the Multilin to stop the pump, which is implied by your question.

You need to clarify your design concept. The circuit in your example is a common way to control a pump with a wet well. A typical design has the Multilin as a motor protection relay, with one of its output contacts in series with the motor starter coil, just as you would put an E-Stop switch contact. You would not normally run the level switch to the Multilin, although you certainly could make that work.
 
Last edited:

Similar Topics

dear, i was looking at the datasheet for rotary paddle limit switch, it says that the switch output is potential free changeover contact (SPDT)...
Replies
3
Views
1,779
dear, i am assigning start/stop levels for the sump pump, i was wondering what is the minimum differential level that can be used when a float...
Replies
8
Views
2,573
Dear all, i have LS1200 murphy used for suction scrubber (connected NC contacts to 1756-IQ16 card) and the question is: when i triggered switch...
Replies
2
Views
1,729
Hi Guys, I wrote a Program on Tank Over fill Protection system. There are Five Tanks/Five Rosemount 2120 Level switch inputs and One Audio...
Replies
2
Views
1,568
Dear, I have a case where a centrifugal pump is sucking from a double compartment tank, usually for the dry run protection of the pump, we use...
Replies
15
Views
7,705
Back
Top Bottom