Logging data fast in AB-L36ERM
frandESS
Sep 2022
Norway
Dear all,
Im using Allen Bradley Compact Logix L36ERM as a PLC.
and facing a problem where I need to create a FIFO buffer that fills an ARRAY[200] that are REALs.
Background: Running Fast Frequency Response (FFR) as a service by our energy management system requires rapid logging for Transmission Line Operator (Electric).
Task:
If action A is triggered, the Variable X needs to be pushed into an ARRAY that is later collected in an IPC and out as a response in an API query. The API response is the ARRAY[200]
Logging interval of each REAL shall be 100mS. I just see that i might will run into scan time and timer issues with this method. Do you agree that an external logger of type PLX51-DL-232 would be better fitted for this purpose or has anyone succeeded with the task above.
Some example code that does it purpose for now, however greatly affected by ScanTime/Task/Timers
FFR_CTD_Array.PRE:=199;
FFR_Timer_Log.TimerEnable:= FFR_Triggered;
TONR (FFR_Timer_Log);
CTUD(FFR_CTD_Array);
IF FFR_Timer_Log.DN AND FFR_Triggered AND NOT FFR_CTD_Array.DN THEN
FFR_Data_Buffer_Frequency[FFR_CTD_Array.ACC] := IV_HZ.Value;
FFR_Timer_Log.Reset:=1;
FFR_CTD_Array.CUEnable:=1;
FFR_BR:=1;
else
FFR_Timer_Log.Reset:=0;
FFR_CTD_Array.CUEnable:=0;
FFR_BR:=2;
END_IF;
IF NOT FFR_Triggered THEN
FFR_CTD_Array.Reset:=1;
FFR_Timer_Log.EnableIn:=0;
FFR_BR:=3;
else
END_IF;
I have completed several FFR projects, using Janitza UMG 512 Pro, at 10mS granularity (spec calls for 20mS, but the default in the 512 is 10).
I could not find a Power Meter I could poll externally (e.g. into a PLC), faster than 200mS.
How often does that Hz value get updated ? What kind of instrument is it coming from ?
What is the event that triggers the 100 ms log ?
ControlLogix has pretty decent physical event task triggers (for general purpose industrial stuff; it's not purpose-built for electrical distribution), and the Periodic Task operating system interrupt will be much more precise than a TON timer in the main Continuous Task.
We are using an ACCUVIM II Powermeter. Responsetimes better than 100mS. We collect data from MB-TCP at a scanrat of 80mS from the unit. @Ken_Roach
Have you verified, i.e. using an Omicron 356 etc, that the Accuvim is able to publish a change of frequency at the rate you desire?
In my early testing, whilst I was able to poll a Schneider power meter on Modbus TCP and get a response every 1 mS, the values were not changing.
Also, in the two TSO jurisdictions I have implemented FFR, there is a requirement for T-5 event data. This means you must record all the time, to have the ability to get the T-5 data once the event occurs.
Hello guys, this is my first post on this forum and i hope u can help me. Im doing a project where we need to read data in the Wincc Professional...
1,043
Hi folks, I'm not as accustom with Siemens & WinCC, however I've been asked to increase the amount of data an existing application is logging...
67
Hi, Wy we log data in PLC using DLG instruction, when we have option to log data in HMI
80
Hi everyone id like to start by saying im not a PLC programmer so my technical terminology is limited. i would like advice on what software is...
299
Hi All, I am looking for recommendations for a data logging software package that can be used for a simple 1 PLC installation. The installation...
1,384