Hello,
I have following hardware:
S71214C CPU, CP 1243-1 for IEC 104 and Energy meter Sentron PAC3200. My Client at very beginning wanted me to transfer data from Sentron PAC via IEC 104 to utility master.
Once we have performed that he wants me to provide data logger for couple of days ( let's say 5 days) 100Bytes. These 100 bytes needs to be saved every 20 sec somewhere. So in 5 days that would be 2.1MB of data. Here is 4MB Simatic memory card for s71200 CPU series
6ES7954-8LC02-0AA0 . Will this be enough for this task or I need something else to perform this?
My alternative7second solution would be to provide small touch panel with USB stick. In that case I would store data on USB stick and read it on Touch Panel first and later on PLC.
Do you guys have something more clever in mind?
If you want to store the data in the PLC, there are larger size cards available for the S7-1200 as well (24MB, 128, 256 and 1GB and probably others). You would save and store the data in load memory in the PLC. If you use the logging instructions, you can save to a csv file in the load memory and read and download directly from the webserver.
You could also do logging via HMI, and usb stick as suggested. At your time scale of 20 secs either would work fine.
Hello all, I'm currently using TIA Portal v17 with a S7-1200 and a KTP-400 Basic HMI. I have a data log set up that begins logging various data...
1,203
Hello Dear engineers; I'm using a comfort panel (Tp1200) in conjunction with CPU-300 (Siemens brand) and TIA PORTAL V.13. I've searched among...
8,714
Just wanted to see if anyone here has experience with this? I have been trying to implement some over the last week or so, and its not working...
2,563
Hi, I am looking to build a system using an s7-1200. I need to log the value of an analogue input. Can anyone tell me if this is possible...
2,957
Hi folks, I'm not as accustom with Siemens & WinCC, however I've been asked to increase the amount of data an existing application is logging...
80