Logix5000 - Cannot See Ladder Logic When Online.
Iangwf
Sep 2010
Castlemaine
Hi all
I have an usual problem with Allen Bradley RSLogix5000 V17.01
When I open a project and it is off line I can view the ladder logic in all routines. Great.....
When I go on line the ladder logic disappears and the ladder area turns grey. This is a project I worked on and saved a couple of hours prior to the problem and all was good.
Can any one tell me what has happened and why I cannot see my ladder logic when on line.
Your help will be appreciated.
Hi All
I've just found out that this issue is most likely caused by the firmware and I should update from 17.01 to 20.04.01.
Thanks all for looking.
Iangwf
If I may...
A firmware upgrade is a relatively big step to take for an issue that might be solved using much simpler steps...
494817 - In RSLogix 5000 All my routines are greyed out when Online
Access Level: Everyone
Have you tried a "good old" software reset?...
Hold down Ctrl+Shift while opening RSLogix 5000 and keep them pressed until it is fully open. This performs a reset of the User Settings for the software.
I would then check again if the routines are visible while online.
Who or how were you advised that this may be a firmware issue? I'm not saying that it is not. I am just curious to know?
Regards,
George
Hi Geospark
Thanks for the reply.
I was informed about the firmware upgrade from a ex Rockwell engineer who now works for the Australian Rockwell distributor.
I read the tech note you referred me to and it looks very interesting, for some reason the problem has rectified it self over the weekend. When I get the same issue I will give the Ctrl+Shift a try to see if this helps.
If I have any developments on this issue I will let you know.
Thanks again.
Iangwf
Hi all, I am attempting to communicate between PC and AB compactlogix L32E Using Logix 5000. FTLinx is able to communicate via ethernet. FTLinx...
1,847
Folks, I have an existing 1756 Backplan with 3 existing modules, no I added 1 more IF6I/A module, RSLinx detected module, RSLogix5000 wont show...
2,829
Hi Guys, Has anyone experienced errors while attempting to delete an Add on instruction in RSLogix 5000 V16.00? I have removed all logic...
61
Hi! So my problem is a little funky, I had Studio 5000 v 24 and 30 installed, but forgot to install RSLogix (which I cannot go without). Is there...
123
So I had an odd request from a customer for the above. I have written the logic and tested it all in one PLC with only using 7 outputs and 7...
428