Logix5000 PID minimum control value question
defcon.klaxon
Feb 2015
Far NorCal
616
Hi all,
I have a PID loop in an AB ControlLogix processor and what I'd like to do is make sure that it doesn't all the CV to fall below a certain value (say, 50%). In the setup dialog box under the Scaling tab, there is the ability to put min and max CV values but I'm a bit confused at what they're asking. It asks for Max (at 100%) and Min (at 0%). Is that as simple as the upper and low limits for the CV, or is there more to it than that? The at 100% and 0% makes me wonder if that's going to affect some sort of scaling, but maybe I'm just overthinking things. Thanks for the help!
It's just that easy. If you specify a lower limit on the CV, it will maintain that value. I often use that as a redundant low setpoint for VFD well pumps, as the pump requires minimum speeds.
OK great, thanks Robb. Yeah this is controlling a VFD and minimum speed is exactly what I'm trying to adjust.
As I mentioned, you may want to put a minimum speed as a parameter in the VFD directly, in case someone or something overrides your PID values in the future. It hasn't never happened to me...
Hi, I am working on control level project using PLC 1756-L62 (Rockwell). I put the same parameters on a MATLAB PID and PIDE of Logix5000...
1,652
Hello, I have a program that monitors pressure in a manifold discharge pipe. Pressure in the pipe should be less then 7.5 PSI. If the pressure is...
17
12,760
Hello all, I cant figure out why my PID is oscillating between 0 and 100 percent. My set point is steady and whenever I take my PID out of...
3,475
Greetings from Michigan, I want to use a PID instruction to control simple oil flow in one of our machines, that obviously uses an oil pump and...
1,655
Hello, Question: (Temp is whats being controlled here by 3 fans) Using a PID; can I set my output (CV) to be 100% at a specific input (PV)? In...
2,248