Tomasek,
1. Download the attached "Batch Simulator-Tomasek" ZIP file.
2. Unzip (extract) the LogixPro file and save it on your computer.
3. Start LogixPro and "Open" the file.
4. "Download to PLC" .
5. Select LogixPro menu "Simulations", then "Batch Simulator"
6. Set Thermostat at 48 degrees
7. Set A-B-C Selector switch to "B" for Continuous operation, (A for one batch).
8. Switch from "Program" to "Run" mode.
9. Press "Start" button.
Once you see that the program runs, then go back and figure out why it works (where yours does not), then look for ways to improve it. For example, I scrambled the rungs to match YOUR last program, but it should be obvious that they should be ordered by the STEP numbers.
Also, try to find why the tank High Level switch does not go on. Hint: You made a slight error when you rounded off the Setpoints for Flowmeter 1 and Flowmeter 2. The "High Level" is 306, not 305, so you need to increase one of your setpoints by 1 in order fill the tank completely.