I have a TSX CFY11 talking to a XBT FC022310. The Touch Screen is showing a fault that lists as follows.
APPLICATION ERROR 1494
CS. 0x210 EIP 0xB
The touchscreen is not communicating with the PLC and if I swap out to an identical touchscreen from another unit it works fine.
I have zero experience with Schneider/Modicon but a little googling has led me to beleive that a) This touchscreen is obsolete, and b) the software used to program it has been superseded by a newer product.
Question 1: Does anyone recognize this error code, and is it recoverable?
Question 2: Is there anyone in North America that could repair this touchscreen if the fault is nonrecoverable.
Question 3: Does anyone know where on Schneider's website one could download the manual for this series of TS's (I found the manual for the replacement XBT-GT but I am guessing that I would need the manual in order to sort out the reset procedure[assuming there is one:smas:])
PS: I occasionally get the following error as well
APPLICATION FATAL ERROR 203
Followed by
WAITING FOR XBT-L1000
For those who are interested.... The problem was finaly traced to a failing memory card. Temporarily solved the problem by downloading the files off of the card, reformatting the card and reinstalling the files back onto the card. Customer is deciding whether or not to replace the touchscreen or to replace the offending memory card.
Lots of these older MAgelis HMIs are in service. Just a note, when upgrading to the newer replacements, though the mounting format is identical, the the newer s/w is not able to import the older L1000 panels and the application has to be re-created from scratch.
I've been tasked by my supervisor to make a connection and do some testing with Vijeo-Designer (Web Gate specifically) and a Magelis Touchscreen...
6,985
I am having trouble running the application throught my PLC, tm221me32tk with magelis HMIGTO6310 I have prepared the plc programme, also created...
118
Good morning friends. . We are having a problem with one of our machines that have two HMI consoles connected to the same network. They have...
1,130
I am looking at a bakery oven that has been dismantled and in storage for unknown time, it was manufactured in 2012 so not that old. my gig is to...
3,631
Any regular users of the magelis range? If so, anyone have a slick way to do a common popup with a rockwell UDT? My current approach is to just...
1,669