Hi Guys,
I'm running S7 315 2PN/DP + KTP1000 HMI and controlling an oven. I have temperatures displayed and set-points sent to controllers. When customer switches off the SP values are lost and have to be re-instated. How can I retain these values? I'm using MW's to write to the PLC should these be MB's?
Can anyone help please.
Cheers,
Norm
Control panel Builder
Report Post
 
Many thanks for the link. On accessing the retentive tab of the CPU properties I find that the boxes where I insert the DB20 say, is 'greyed' out. Any ideas how I might insert these parameters?
 
Thanks for your response. My TIA Portal does not have a retain tab. It looks as though that option is for 1200 plc's and not S7-315. I have wincc Basic V11 SP1. That apart, I would have thought that the values would be installed in the HMI. I have not come across this problem with AB or Mitsi or Fuji HMI's. Any othe ideas?
Regards
 
ok, now for the 300 series :)

in cpu properties/retentive memory you can assign which areas are retentive starting from MB0. default is MB0 to MB16 (315 1.jpg)

When using DB`s the retain value is by default checked (315 2.jpg)

i hope this helps

315 1.jpg 315 2.jpg
 
Thanks for the two views - that would be the answer if I had used TIA to program my plc. I used step 7 V4.5 to program plc and TIA portal for the HMI. My data blocks are in step 7.
Do you think Is there an answer ?
Regards
 
Ok, go to HWconfig and then the retentive memory tab. There you can specify the number of memory Bytes that are retentive. It`s the same as in tia portal.
Default MB0 to MB16. So when your values are stored in MB/MW 20 they are not retentive with the default settings.
You could consider to transfer you values to something below MB16 or adjust the hw config to your preffered needs.
im not familiair with the "areas" part in this tab so cant tell you anything about it :p

Datablocks are retentive by default, but there is an option to make m non retentive.
right click on a DB --> object properties --> then click the general part 2 tab.
There you find a checkbox non retain

s7.jpg
 
Thanks for that. That looks promising. I have modified the default settings in the box above. I will try this next week and let you know how I get on.
thanks again
Norm
 

Similar Topics

Hi folks ! Got an older Modicom BM85 and I suspect that it's not passing data to ModBus+ network. We had a power loss for a few days and I suspect...
Replies
0
Views
70
We have a machine that keeps losing its program at random intervals; sometimes 2x-3x in a shift, sometimes will go over 1wk without issue. I had a...
Replies
9
Views
2,950
Has anyone experienced any retentive memory loss on recent Red Lion Kadet screens (G307 in particular)? The equipment in question has a G307K200...
Replies
1
Views
2,115
Hi. I have some (quite basic, actually) questions: 1) Does anyone know exactly what happens when you perform a Memory Reset on a Siemens S7300...
Replies
1
Views
1,444
HI All, I am experiencing one problem for few months which i would like to share with you experts. My SLC and Micro Logix Controller especially...
Replies
6
Views
3,404
Back
Top Bottom