ML1100 D.I. causes memory loss
strantor
Sep 2010
katy tx
401
We have a machine that keeps losing its program at random intervals; sometimes 2x-3x in a shift, sometimes will go over 1wk without issue. I had a hard time getting a new battery for it, took over a month. After receiving and replacing the battery it continued to lose its program, so I have a new PLC on order.
As I'm waiting for the new PLC to arrive (Micrologix 1763-L16AWA) I received a report from operators that the PLC loses its program every time they push a certain button. It's a button for a manual function that only gets used in one certain situation, not very often. I hear this and it sounds like nonsense. I've never heard or seen anything like it and my first instinct was to write it off, but i went to investigate nonetheless and found it to be absolutely true. It's a simple circuit: 120v>wire>button>wire>Digital Input. I tested for shorts, grounds, etc, nothing. All good. That digital input is bad, I tested by disconnecting the button and running a jumper from 120V to the input, and as soon as it sees that input it pukes the program.
Just curious if anyone else has seen this before. Total curveball for me.
Not quite the same problem but we had a machine that every time a certain button was pressed the plc would re-boot. I also traced this to a certain input I also tried to remove the wire and link it to the supply & the same thing happened. It turned out to be a shorted solenoid coil that took the supply low when the button was pressed i.e. it was not the input but an output that was turning on when the button was pressed thus causing the plc to fault then restart.
I suggest that this could also be a cause although in your case it is spiking the PLC causing corrupt memory, I do know someone who had this problem on an old SLC that were prone to spikes causing program loss.
I've shorted the pins to each other on a OW16 expansion card (don't ask) and had the PLC lose it's memory. I would also move the input and see if the problem follows.
I have had AC powered ML1100's lose their marbles if there is a "brownout" feeding the power supply. Make sure that notorious button is not suffering from some other electrical issues that is causing a droop on the voltage feeding the brain. I have a preference for DC powered Micrologix partly because of this.
Sounds as bad as SLC500's they were prone to that, although I have never lost a program on an 1100 or 1400 personally.
I have a brand new one here that anytime its powered down it will lose the program and faults out... but out of the hundreds I have used that is the first one so I am not complaining at all, they are electronic and are going to fail someday it's just a matter of when.
When you say "loses its memory" it would be in fault mode then, Do you read the fault before reloading the program. I have seen this before a lot on the ML 1000's with a retentive data loss fault or something similar. I was told suppression on outputs, poor grounding or poor supply power.
It runs fine, never faults and does everything it should, until.... you power down, once you power up again everything is gone and the fault light is flashing, I did look at the fault but forgot what it said, I think something about memory, I even tried loading a MM1 but that did not help and would not let the program reload until you cleared the fault, I put it up for sale on Fleabay, figured someone could use it as a trainer or a test PLC
https://www.ebay.com/itm/373223496405
I'm looking to implement a low-cost, efficient method of communicating some integer values to an R30iB robot from a Rockwell 1100 PLC. I am not...
1,726
Hello all, I am trying to setup my MicroLogix 1100 as a modbus RTU master for a modbus network containing multiple modbus RTU slaves. I currently...
3,928
Just asking for clarification here, but from my research all I need is a 500 ohm resistor across the AI and the common? Heres my schematic. I...
2,586
I have a CLX L61 and I'm trying to read from and write to a Micrologix 1100. I'm attempting to read 200 REAL elements but I'm receiving an error...
1,459
Hi all, I've been tasked with migrating a standalone control box with a Micrologix 1100 into an existing 5380 Compact Logix controller. It has a...
2,431