Messaging between CLX PLC
raul_vaze
Feb 2008
mumbai
87
Dear All ,
We have around 10 PLC-5 System which we are upgrading to Control logix V19.0
Now these PLC used to exchange data between them , so we are planning to use Message instruction .
We gotta some feedback that for messaging it is required that the Data type should be DINT and not INT .
Is it true that the Data type shall be DINT always for messaging between CLX PLC as there are some existing PV1000e connected to this Control logix PLC (since previously they were connected to PLC-5 on controlnet) and data type there is INT
PLC-5 controllers can easily exchange INT data types with ControlLogix using the MSG instruction.
Some older PLC-5E controllers and 1785-ENET "sidecar" communication modules do not support the CIP Ethernet, aka "EtherNet/IP" messaging protocol used by ControlLogix.
A full list of the required Firmware revisions for each hardware Series of the PLC-5 is in RA Knowledgebase Article ID #19325 (Access Level: Everyone).
All PLC-5E controllers can be upgraded but some older ones require a physical firmware chipset to be installed. I believe that Rockwell Automation is no longer offering these as field kits but rather only as part of a remanufacturing process.
...I believe that Rockwell Automation is no longer offering these as field kits but rather only as part of a remanufacturing process.
Just went through it and you are (as always) correct. Its a policy that must have been instituted within the last year or so because most of the people I spoke to in the distribution channels thought that update was still available and perhaps even at no cost. Sadly that path is not an option any longer. You must spend around $1500 (plus downtime) to have the PLC-5 reworked. In my case it was cheaper just to replace it with something else.
Which is probably the reason for the new policy in the first place.
I have followed several videos and tutorials that suggest when using the MSG function to enter 2,xxx.xxx.xxx in the Path box in order to connect...
1,387
Hi, We have an existing ControlLogix Processor (Rockwell PLC) and we want to replace it with either an quantum or Unity Processor (Schneider PLC)...
3,208
Hey guys, I'm trying to set up messaging between two PLC 5 processors that are on Data Highway, but I'm having a difficult time finding any...
1,468
Having a little trouble messaging between to old plcs at my mill. I’m trying to message between a PLC-5/40B and PLC-5/40E on a data highway...
3,377
Does messaging work between a SLC500 and AD DL06 plc? I want to be able to monitor some outputs from the SLC500 and use them as inputs to the DL06.
1,547