micrologic 1100

siggibald

Member
Join Date
Oct 2012
Location
iceland
Posts
60
hello

i have a micrologix 1100 and it have I:0.0 - I:0.9 input, bud i can only se I:0.0 - I:0.3 in rslogix . and same with the output, the plc has O:0.0 - O:0.5 bud i can only se O:0.0 - O:0.3 why is that ?
 
Last edited:
Then you must have the 1763-L16AWA model because it is the only ML1100 with 10 built-in 120 VAC inputs.

Where are you "seeing" the 4 inputs? Did you click on the left tree menu, "Data Files", then "I1 - Input". All of your configured Inputs should show up in the list. At other places, only the USED inputs show up.
 
Last edited:
When you write I:0.0 - I:0.9 I think you really mean I:0.0/0 through I:0.0/9 meaning the ten discrete (On/Off) inputs. These would be the ten '0' (or '1') in the top row under the 0 - 9 columns.

Similarly in the output display what you write as O:0.0 - O:0.5 are actually O:0.0/0 through O:0.0/5 and are the six '0' (or '1') in the top row of that display under the 0 - 5 columns.
 
Last edited:
When you write I:0.0 - I:0.9 I think you really mean I:0.0/0 through I:0.0/9 meaning the ten discrete (On/Off) inputs. These would be the ten '0' (or '1') in the top row under the 0 - 9 columns.

Similarly in the output display what you write as O:0.0 - O:0.5 are actually O:0.0/0 through O:0.0/5 and are the six '0' (or '1') in the top row of that display under the 0 - 5 columns.

correct i see it now o_O
 

Similar Topics

Is there any way to change the SMTP port on a Micrologic 1100 PLC to send Email from another port besides 25. My ISP blocks port 25 and I would...
Replies
0
Views
1,643
Hello All. Have set my IP address setting on 1100 using serial connection and when I recycle power everything is ok not until I put it on the...
Replies
8
Views
3,965
need to access micrologic 1100. when trying to access to pull program out for future use to save for backup I can see it in rslinx but it says it...
Replies
10
Views
4,500
I keep getting disconnected when I try to do online editing on the few Micrologic 1100 we got. At first I thought it was because of the older...
Replies
2
Views
5,538
Dear all, Currently i'm working with micrologic 1400 cpu and Temate G5 Controller. I plan to communicate micrologic with temate using...
Replies
0
Views
403
Back
Top Bottom