micrologic 1100
Dec 2008
indiana
24
need to access micrologic 1100.
when trying to access to pull program out for future
use to save for backup I can see it in rslinx but it says
it does not recognize the processor.
does that mean I need a different driver or updated software
for the slc500 software?
This is company software and company equipment so if I need to
purchase something I can,but just need what I need.
Thanks Mike
Note I have on several occasions uploaded and downloaded with
micrologic 1000 that the company has if that helps.
1100 is Ethernet connected. just make sure the IP address and subnet in your computer are set to that of the processor and it should pop right up in linx using ethernet/IP driver
Not necessarily. There's no mention that he's connected over Ethernet. He could be connecting with a PM cable.
In any case, it may just be that he doesn't have an EDS file for the ML1100.
See below for software requirements. ( From AB knowledgebase)
37951 - What software is needed to support the MicroLogix 1100?
RSLogix 500 release 7.0 or later
RSLinx Classic release 2.50 or later
Also, RSLogix Micro version 8.10.
RSLogix Micro Starter Lite is available for free download to program the ML1100.
Micro Starter Lite
Series A: RSLogix 500 ver 7.00 RSLinx ver 2.50 Series B: RSLogix 500 ver 7.20 RSLinx ver 2.51
Contact your local AB rep.
version of rslogic is 6.3 and rslinx is 2.43.
What is a eds file?
I connected over the 232 cable I use for the micrologic
1000 and it saw it.
Thanks for all the responses.
Mike
The correct answer is above in this thread; your RSLogix 500 version 6.3 (released August 2004) will not work with this MicroLogix 1100 controller.
The only thing you need to purchase is a TechConnect contract, if you do not already have one, in order to be eligible to download the current release of RSLogix 500 and RSLinx Classic software.
An update is an update for your RS Logix 500. My suggestion is get a Tech Support package from your local AB rep. Since you already have an exisiting copy of RS Logix then this is the most cost effective route.
EDS is the file that RS Linxs uses to see various PLC's online.
This too can be upgraded thru your AB rep.
hello i have a micrologix 1100 and it have I:0.0 - I:0.9 input, bud i can only se I:0.0 - I:0.3 in rslogix . and same with the output, the plc...
1,848
Is there any way to change the SMTP port on a Micrologic 1100 PLC to send Email from another port besides 25. My ISP blocks port 25 and I would...
1,644
Hello All. Have set my IP address setting on 1100 using serial connection and when I recycle power everything is ok not until I put it on the...
3,966
I keep getting disconnected when I try to do online editing on the few Micrologic 1100 we got. At first I thought it was because of the older...
5,538
Dear all, Currently i'm working with micrologic 1400 cpu and Temate G5 Controller. I plan to communicate micrologic with temate using...
403