micrologix 1100 modbus powerflex4m
May 2006
huddersfield
67
HI
I have 2 pf4m drives connected on modbus to my micro1100 all is working fine although i have noticed one thing.If you turn off the first drive (node 1) then my second drive stops.I can alter the comms loss action to continue last action, this is ok but i really need the second drive to start and stop when requested even if the first drive is powered off.Does anybody know of a way of configuring either the plc or drive to do this??
Regards
Alex
when you say powered off - do you mean de-energised completely.
If so - Why -
the comms are checked so there is probably a fault because os a missing node.
The PLC program is responsible for monitoring messages and taking appropriate action. If one drive being powered off while the other continues is a routine occurrence then the program should have some method of detecting this (either by inputs or by monitoring a message error) and making the appropriate changes in the messaging.
Hi i am simulating what would happen if the drive mcb trips.I have managed to sort it.By enabling the ignore timout in the messages for drive 1 if there is a fault with drive 1.Thanks for your help
Hey everyone, Ran into a bit of an issue with a Modbus RTU radio link on a MicroLogix 1100. Just for context, we have a remote lift station with...
31
13,573
Hi everyone, I have to read some data via Modbus from a device that only has RS-232 ability. I purchased the 1763-NC01 cable but from what I am...
1,384
Hi All, Just wondering if anyone can offer some help or point me in the right direction in regards to Modbus communications between a Micro820...
5,304
Hello! Sorry with have some errors! I'm using micrologix 1100 powerflex 4M IHM, and I will do the temperature control using PID. I will...
2,381
-Channel 0 as the modbus master port -8 slaves (Yaskawa VFD's) on a RS-485 multi-drop network -I can talk to the slaves (Yaskawa VFD's) through MD...
9,855