MicroLogix 1200 Controlling 2 PowerFlex 4M VFD's
tombonas2009
Jul 2009
New York
Hello Everyone. A friend recommended me to this site. I have a few questions:
Here are the parameters I set on the PowerFlex 4M VFD's
P105[Start Source] = 5 Comm Port
P108[Speed Ref] = 5 Comm Port
C302[Comm Data Rate] = 4 (19.2K)
C303[Comm Node Address = 101 for VFD #1 and 102 for VFD #2
C306[Comm Format] = 0 (RTU 8-N-1)
The Dip Switches on the 22-COMM-E are set to Multi Drive.
From here I am not really sure where to begin. How do I message to the PowerFlex 4M's to get Reference, FeedBack and Control(Start/Stop)? They are on RS485(DSI). All the samples and documentation from Rockwell show a PowerFlex 40 with Ethernet messaging.
Where did you find this example of a hook-up? From MicroLogix 1200s we use an RS485 converter and MODBUS to talk to these drives. It works great.
I actually used the 22-xcomm base but it was a devicenet version. It was not very straight forward how to set it up, and not having a whole lot of experience with these, I had to get some help from our distributor's rep. I used a ML1500 with a deviceNet card in the I/O. I was actually addressing to the xcomm-base, and the drives showed up as different nodes (programmed manually in each drive) in the 22-xcomm-base. I never used the Net-eni module, and I am not sure you can set up your addressing through that to the 22-xcomm-base which will house your two drive nodes. I set it up using RSNetWorx, and was able to use that to help me set up the structure in RSlogix 5000. I don't know how you would message to it in RSLogix 500 either since you are using a ML1200.
I have a poerflex 4, micrologix 1200 firmware 12 series connected with a 1761-NET-AIC converter. I followed an example from rockwell website, it...
3,998
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
659
I have a MicroLogix 1200 that has an 8 input and a 16 output. Every 6 months-year I get a fault and when online go to error it is something like...
511
Have a bad output on a Micrologix 1200. Moved wire over to an available output, changed program to associate with new output. downloaded program...
756
I need help achieving the following task: ML1200 sending 4 to 20 mA thru analog output ch0 to a DC speed controller analog input(4 to 20 mA) my...
673