I am currently trying to connect a MicroLogix 1200 PLC (1762-L40BWAR) to a Prosoft Profibus Master/Slave Gateway module (5105-DFCM-PDPS). The questions I have for anyone who has dealt with this configuration are:
  • Do I set the DF-1 port 0 to a master or slave?
  • Does the PLC have to send signals or does the Gateway device take care of this?
  • Is there a way to find out if the signals are being sent between the devices without a Profibus Master unit controlling the Gateway?
I have tried calling the Prosoft technical support, but I cannot get any help since they have been very busy lately. I am new to these type of devices, so please bear with me if I made a jargon mistake. If anyone can help, I will greatly appreciate it. Thanks.
Regards,
Nik
Niko..
The DFCM (DF1) driver can act as the master or slave. If you set the DFCM driver as the master, then you wouldn't have to modify your logic.
If you setup your DFCM commands to communicate with the ML1200, then on the ML1200 side, you shouldn't need to do a thing other than ensure the port settings match.
Using the diagnostic tools, the 5105 gateway has a built in data analyzer that enables you to see the raw DF1 traffic going between the gateway and the ML1200. It also has a data map that allows you to see values you're sending/receiving. For instance, if you setup a DFCM command to read from N7:0 (that has a value of 1234) on the ML1200, then you'll be able to see this value of '1234' in the data map.
About Prosoft being to busy to help, call your distributor or local Prosoft rep and explain the situation.
CH
Hi y2kmfic,
Thanks for you reply.
I did figure out how to get them to communicate. My main problem was that the error protocol on each end was not set to the same protocol! A simple mistake, but when you're doing this for the first time, and easy one to overlook.
Prosoft did eventually get back to me and were very helpful.
Regards,
Nik
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
655
I have a MicroLogix 1200 that has an 8 input and a 16 output. Every 6 months-year I get a fault and when online go to error it is something like...
510
Have a bad output on a Micrologix 1200. Moved wire over to an available output, changed program to associate with new output. downloaded program...
755
I need help achieving the following task: ML1200 sending 4 to 20 mA thru analog output ch0 to a DC speed controller analog input(4 to 20 mA) my...
673
Hi there I am new with this thing and i don't know how to connect Allen Bradley Micrologix 1200 PLC to Raspberry Pi using USB to RS485 in NodeRED...
2,282