I have an expansion I/O module 1762-IF4 that I have added to my micrologix 1400. I am attempting to monitor temperature readings from 3 K-type thermocouples. I have tried in vain to set up this module to display accurate temperatures, but so far I have struck out. Can someone tell me the best way to setup/monitor the data so I can get accurate temperature readings. I'm not vain, so I'll take any suggestions from the most basic to whatever works best. Thanks.
 
If you only have a 1762-IF4 then you are going to have to convert your thermocouple to
an analog signal ( transmitter). That card only accepts voltage (-10 to 10) or current ( 4-20ma). Most transmitters will convert your thermocouple to 1-5volts, 4-20ma, 0-10volts.
You can then use scaling instruction(s) to give you engineering units ( temperature)
within your PLC.

Or as posted by others get a card that accepts thermocouples directly.
I prefer the 1762-IF4 myself, more flexible unless you are going to fill the thermocouple card up ( use all it's channels)
 

Similar Topics

Hello everyone.Am new in allen bradley configuration,i have a mini project to execute, i have wired my Micrologix 1400 for analog input signal of...
Replies
0
Views
1,515
Hello everyone.Am new in allen bradley configuration,i have a mini project to execute, i have wired my Micrologix 1400 for analog input signal of...
Replies
3
Views
2,620
All, I need some assistance ASAP. I am not sure how to configure IV3+ analog input for 0-10 vdc. Is there a jumper or something that I need to...
Replies
2
Views
1,402
Hey I'm a student working on a project. I trying to control a 0-10V driver using the analog output on the ML 1400. To test and output I've been...
Replies
26
Views
9,448
Hi everyone! I have a micrologix 1400 with an 1762-OF4 analog input module and I'm trying to wire a vacuum transducer outputting 0-10V to it. 0V...
Replies
11
Views
3,556
Back
Top Bottom