Hi, if you need to increase or decrease the speed of the motor when Speed Set Point is 100%, then you need to change the parameter P1082 (default setting to 50Hz).
The range of P1082 is 0-650Hz.
Anyway I attach the follow picture about the P1082 data sheet for additional information.
It's extracted from the MM440 Parameters List Guide.
Regards
Welcome to the forum.
I find your question a bit vague to be able to give a specific answer.
1: Which speed function is it?
A: Setpoint?
B: The max speed? (see post above from cagliostro)
C: The min speed?
D: The speed scale reference?
E: Other?
2: How do you want to change speed?
A: From the panel front?
B: From the digital inputs?
C: From the analog input?
D: From preselected setpoints?
E: Via USS?
F: Via Profibus?
G: Via Canbus?
H: Other?
Kalle
hi kalle,
i have checked through the panel front and found this reading
p0003=3
p0010=0
p0100=2
p0300=1
p0304=400v
p0305=5.6A
p0307=2.2kw
p0308=0.7pf
p0310=60HZ
p0311=1140rpm
p0700=6
p1000=6
p1080=10HZ
p1082=60HZ
p1120=120s
p1121=120s
please suggest me how can i change the current speed 30 HZ to 50 HZ.
Do you have the parameter manual?
P1000=6 means that the setpoint comes from the communication card, most likely a profibus card.
The speed must be changed from the (profi)bus master.
You can change the P1000 to another setpoint source, BUT THIS COULD BE DANGEROUS.
Kalle
Edit: What kind of machine is it? (conveyor, fan, pump, elevator...)
thanks for your information, it is a fan motor, ....
Can u please suggest me how to change through the profibus master.
And please tell me what kind of failure it may happen if i change P1000 to another set point.
I agree with bornwild.
Why it can be dangerous? I have to assume that, since I don't know anything about your process.
Perhaps there are some unwanted actions starting if the PLC reads a speed above 30Hz.
If you are certain it will not damage anything, you can do a quick and dirty fix by changing the minium speed in P1080.
Kalle
Edit: Normally I would expect there is a PLC running as bus master, and that the fan is controlled by a PI(D) or by a fixed setpoint coming from an operator via an HMI screen.
If it's controlled from a PI(D), could one imagine that a pressure or temp. transmitter is malfunctioning, and your fan is running at the controllers' minimum speed?
My tutor asked me for this small project: using S7-200 control MM440 with PROFIBUS. Because S7-200 with PROFIBUS module EM277 can only be PROFIBUS...
3,007
fault A0501 (i.e current limit ) displaying whwn i replace siemens 420 drive with mm440. all parameters are crosschecked. please help to...
1,582
I have a Siemens Micromaster 440 (6SE6440-2UC25-5CA1) with encoder module (6SE6400-0EN00-0AA0) and Profibus module (6SE6400-1PB00-0AA0). I'm...
3,085
Hi All I have the SIEMINS micromaster 440 not starting good several times then start after 1 to 2 hours . so I took the AOP kit and opend it >>...
4,510
Dear all, We are working with MM440 at th plant where i'm working. The MM440 is connected to S7 400 PLC. In the hw config the setting is 0PKW...
1,446