Mitsibushi A800 not commnunicating

AbijithVijay

Member
Join Date
Dec 2023
Location
Kerala
Posts
1
Connected and communicated my Mitsibushi A800. Drive to compact logix through A8NEIP 2P module. But when start command is given, drive start button is blinking. In manual shows frequency command is not given or less than starting frequency. Is there any change in parameter setting in drive is required to get the frequency command. How to solve the issue
 
There are several parameters that must be configured on the drive when commanding it via the network, through an option card.

Pr. 340 and Pr. 79 set the Operation Mode. You'll want to configure those parameters to put the drive in NET operation mode.

Pr. 338 is the Communication operation command source (i.e. run command source).
Pr. 339 is the Communication speed command source.
Pr. 550 is the NET mode operation command source selection.

Details on these parameters can be found in the drive's Instruction Manual (Detailed), starting on page 404:
 

Similar Topics

Does anyone have any experience with converting a Beckhoff (codesys) program to a mitisbushi program? Excluding IO of course. Are both on the...
Replies
11
Views
4,023
I am working with Mitsubishi fx3u.. confused with the "SMOV" instruction read through many manuals but couldn't really understand it. what I...
Replies
2
Views
2,576
Hi, I currently using TCP to communicate a mitsibushi QU03 to S71515-2PN. I have succesfully set up comms for send and recieve but on the...
Replies
3
Views
1,652
Hi, I am incorporating a Mitsubishi Q series (Q03UDECPU) and DP Profibus master (QJ71PB92V) to control an ET200M remote IO (32bit Input card = 4...
Replies
0
Views
1,102
Hi fellow PLC folks, I am quite new to the game of PLC's and have some simple questions (sorry if I am annoying anyone with my ignorance here)...
Replies
25
Views
5,910
Back
Top Bottom