Vikkaraja,
I see some errors.
For example, on your Rung 4 you have 3 contacts in parallel with the Cycle Stop pushbutton (tomato counter done, chili counter done, and mixer timer done). You do NOT want to stop the cycle when these events happen. You would only want to stop if the Stop button is pressed, or maybe if the end of cycle is reached. However your instructions say to repeat the cycle, so you do not need anything in the "stop" logic except the stop pushbutton. Even if you did, these contacts would have to be in SERIES with the Stop pushbutton, not in PARALLEL with it. Rung 4 should logically be moved to the FIRST Rung 0 in the program.
On your Rung 2, your tomato counter is set for "10" even though you said you only wanted to use 5 gallons. This will probably result in the mixer overflowing and creating a mess. On Rungs 0 and 1, you did not use the High Level Limit Switch to prevent this from happening. Your logic will keep adding tomatoes until 10 gallons is reached, even if the mixer should only hold 6 gallons!
On your Rungs 5 and 6, the 2 "Counter Done" bits are not needed. You already have those built-in with Counters C5:0 and C5:1. Use C5:0/DN and C5:1/DN and delete B3:0/1 and B3:0/2
On your Rung 9, the Dump Valve only dumps while the High Limit is ON. As soon as the level drops below High, the dump will stop. You want it to continue dumping until the Low Level switch is ON.
Also, all the rungs should be rearranged, so that the logic is easier to follow:
Start,
Do Step 1 (Add Tomatoes),
Do Step 2 (Add Chili Peppers),
Do Step 3 (Mix)
Do Step 4 (Dump),
Repeat Cycle, or Stop.
Here is the way I would do it.