Hi, its been a while since I began to program Micrologix family PLC but everything was way simple. Now I am a bit stuck with the analog Inputs in a 1400 (1766-L32BWAA)
I have 3 similar to practice at school, Last week when I was learning about the input value (for SCL instruction) I was using a variable voltage source instead of a transducer o sensor and everything went fine with the values, I then added a potenciometer and a simple temp sensor (the ones used in mini splits a/c)
But today, working with other of the PLC and the same kind of variable source (cant tell if it was exactly the same device but very identical like a twin) the input value for the analog input was at max = 4060 and the kin I dont remember but was aprox 2400.
I was able to calculate it anyway and make it work but, the source I was using was providing me a range from 0 to 10 V, I even increased it to 15 but the input value remained at 4060, supposedly it would be 32,700 a bit more like last week PLC.
Is there a chance I mistaken any config or setting? I am using the on board inputs I:0.4 to I:0.7 and in all of them the values were the same.
Also, I am not sure if the common to input has polarity, I first connected the + of the source to the common and the - to the input but nothing appeared in the input so I inverted it, did I blew something?
Or by any chance it was a wirinf or source problem?
Also I found a glitch, In the I/O config if i add any analo module to the plc and the read the I/O from the online PLC, that file will always fault me the PLC, even if I remome the module that phisically doesnt exits.
For now those are the questions, I have more but are a slightly different topic.
The resolution of the analog inputs on the ML1400 is only 12 bit (0 to 4096). There is no workaround. You need an analog input card (like a 1762-IF4) to have 16 bit (-32768-32767) resolution.
Also, you should have been careful about what you attempted to input to the on-board analog inputs. From the manual:
Voltage input overvoltage protection 10.5 V DC
So, 15 volts may have not been the best thing for the inputs. Maybe someone else already applied too much voltage and ruined them ...
@FactoryTalk you are right, I had this doubt about the resolutions bits, I tested it today with the other 2 PLC and is working, I dont know how my memory messed it with the values of the first test.
I was developing a small program to calculate rate and offset, but I might have to add options for built in and external cards, and also the raw/proportional and PID.
@Danatomega: Luckly nothing was damaged, I intented 12V not 15, everything is working right on the 3 PLC
Hello everyone.Am new in allen bradley configuration,i have a mini project to execute, i have wired my Micrologix 1400 for analog input signal of...
1,515
2,621
All, I need some assistance ASAP. I am not sure how to configure IV3+ analog input for 0-10 vdc. Is there a jumper or something that I need to...
1,403
Hey I'm a student working on a project. I trying to control a 0-10V driver using the analog output on the ML 1400. To test and output I've been...
26
9,459
Hi everyone! I have a micrologix 1400 with an 1762-OF4 analog input module and I'm trying to wire a vacuum transducer outputting 0-10V to it. 0V...
3,559