ML1100/1762-IF4 Analog Input Help
Tpetie3509
Apr 2017
Washington
23
Hardware:
Micrologix 1100 & 1762-IF4 Analog Input Module
Problem:
I have one 4-20mA transmitter hooked up to I1:0, I am monitoring the current as it comes in while I adjust it. The transmitter is outputting a good 4-20mA range, however the input as it comes into the PLC will stop at around 11.5mA at a raw value of 17673.
I am using a 12VDC power supply as it is a 12V PLC and the transmitter is 10-30VDC.
I can't figure out what would be causing this unless I'm underpowered which doesn't make sense as the transmitter and PLC are rated for operation well within what I am using.
is module configuration set for 4-20? Sometimes defaults to different settings.
Also, wouldnt use a power supply for this. Use a current source.
Configuration is set for 4-20mA.
Are you referring to troubleshooting the PLC? I have to be able to use a power supply out in the field to power the PLC and the transmitter.
My money is on the transmitter power.
Can you provide the make model/catalog number of your transmitter?
Voltage to a transmitter will dictate how much load it will support.
So in order to get a full range reading, am I looking at a power supply of 21.75VDC for the sensor? I'm not quite sure I understand what these specs are telling me.
I would say more like 17 to 18 volts. But I would use a 24 volt power supply for the transmitter.
You need voltage to drive thru your load, the more load ( in your case 275 ohms) the more power (Voltage) is required to drive the 4-20 ma.
The 24V power supply solved the problem, now to figure out how to get that kind of power to a solar powered remote station..
Thanks for the info, I really appreciate it.
I already have a solar panel and battery setup out there for a 12V system. I think I will try one of the converters and see how it does. There is minimal total load on the system. Thanks again for all the info and replies!
Hello, I'm new to analog signals as far as scaling them and what the useable output voltage will be. I need to utilize the 0-10vdc output. I...
5,475
I have a ML1100 with 4 1762 Digital Input expansion modules. Can someone tell me the addressing scheme for these added inputs? Thanks in...
2,755
I'm looking to implement a low-cost, efficient method of communicating some integer values to an R30iB robot from a Rockwell 1100 PLC. I am not...
1,727
Hello all, I am trying to setup my MicroLogix 1100 as a modbus RTU master for a modbus network containing multiple modbus RTU slaves. I currently...
3,928
We have a machine that keeps losing its program at random intervals; sometimes 2x-3x in a shift, sometimes will go over 1wk without issue. I had a...
2,944