Hi Guys, Hoping someone can help me out.
I am trying to read some registers from a Modbus slave. In the MLocation attachment, everything is working fine. When I try to put the read value into a DB I get an 818C error. What is the difference between these two other than one being a M location defined as a real and the other being an array of reals inside a Data Block.
Thanks You
I have used an S7-1500 as Modbus Master, however i wasn't exchanging float values. What i think might be happening, is that even if you defined MD26 as Real (and probably transfering data so that it's actually a real), the block is actually using it as a starting address. So it's starting from MB26 for a length of 2. I think you should try transfering to a word or byte area, and then reading it as reals.
When i first used Modbus with Siemens, i did it by studying an example project that Siemens provided, in which they used a Word array instead of a Real array.
Hope this helps somehow
You may need to pass the whole array, not just the first element of it. Just a guess, never tried this instruction before.
Try "ModbusDB.LIT_101A_Data", with no brackets.
Thinking that location need be whole array without brackets or on p#dbxX.dbY byte xy format.
Also not optimized db block?
Please see the attached pictures. I'm can't figure out for the life of me what I am missing.
Real DB Whole Array.png shows the result I get when passing the whole array.
M DINT.png shows it working with a Memory Location defined as a DINT
DINT DB.png shows it not working when using a DINT in a DB.
MB Table.png is a screen shot of the modbus table from the book. It has the data type listed as UINT32. That would be the same as a DINT, right?
I have tried everything I can think of to get the data into the data block. Initially I thought it was a problem with the DATA_LEN parameter but I have tried 1,2,4,8 all with no luck. I would think that in order to write to an array of 4 reals, I would want a DATA_LEN=8 since when writing to a M real location DATA_LEN=2 gets me the correct value.
Thanks for all the responses
No it is not.
I will try a non-optimized block first thing in the morning.
Thank you
i also agree, the DB should be non-optimized. Otherwise it won't work. If you need an array with an optimized DB, make a "temporary" non-optimized DB and just copy it over to your original DB. That's what i did.
Changed to a non-optimized DB and it is working fine.
Another quick question. Is there an equivalent of the AB CLR instruction in TIA Portal?
Thanks You
What does CLR do exactly ?
If it just sets a single variable to zero, then program a MOVE with 0 or 0.0 as the value to move into the variable..
If it sets multiple contigous variables to zero, then program a FILL_BLK, again with the fill value being 0 or 0.0.
CLR pretty much just sets a memory location to 0.
I am clearing a value the way you suggested, I was just wondering if the instruction was available for future use.
Hi there, I'm using an S7-1200 system and I have followed a Siemens application example to read/write data to 1x slave using Modbus RTU and a...
4,188
86
Does anyone have an example project of the cm ptp ET200 SP HA with 410-5H DCS (PCs7 9.1 SP1) for MODBUS MASTER/SLAVE communication ?
135
I'm using M340 (Schneider Electric) as modbus master. It works fine but if there is a disconnection with the slave, it stops working even after...
430
Hi guys, Just wondering if anyone has tackled an issue similar to this before: creating a redundant master on Modbus so I can have a redundant...
448