MODBUS RTU Help

wdwune

Member
Join Date
Nov 2015
Location
QC
Posts
1
Hi All,

So, I am fairly new to PLC and am trying to learn as much as I can for my job. Currently, I am working on interfacing a PLC to a VFD to access its frequency, accel time and decel time using MODBUS RTU (RS485). It's actually my first time working on MODBUS but I've read (and watched some tutorials) about it.

The problem is, I'm still stuck with a "Host communication Error". I really don't know where to go from here since I think I've searched google for any supplementary files provided by the suppliers of the products and applied them but still no progress. *sighs*

In any case, the PLC I am using is IDEC's SmartAxis FT1A Touch while the VFD is LS-iG5A. Is there anyone here who have worked with these products? Or can anyone share his knowledge with connecting VFDs to PLCs regardless of the product models?

Your help is greatly appreciated. I am really desperate now since I am just learning this all by myself and have undergone no training whatsoever aside from college laboratories.

Thanks in advance!

Best Regards,
wdwune
 
Hi All,

So, I am fairly new to PLC and am trying to learn as much as I can for my job. Currently, I am working on interfacing a PLC to a VFD to access its frequency, accel time and decel time using MODBUS RTU (RS485). It's actually my first time working on MODBUS but I've read (and watched some tutorials) about it.

The problem is, I'm still stuck with a "Host communication Error". I really don't know where to go from here since I think I've searched google for any supplementary files provided by the suppliers of the products and applied them but still no progress. *sighs*

In any case, the PLC I am using is IDEC's SmartAxis FT1A Touch while the VFD is LS-iG5A. Is there anyone here who have worked with these products? Or can anyone share his knowledge with connecting VFDs to PLCs regardless of the product models?

Your help is greatly appreciated. I am really desperate now since I am just learning this all by myself and have undergone no training whatsoever aside from college laboratories.

Thanks in advance!

Best Regards,
wdwune

Since you don't know where the problem is, some data is called for.
I have used 232analyser, by CommFront, http://www.232analyzer.com/232default.htmin the past, for this. It will show the data flow in both directions, if you have the right hardware.
And, in the "OnceBittenTwiceShy" category, I always put some sort of potential-isolator device on the network. CommonMode problems are beyond difficult to troubleshoot, and the isolator simply makes them all go away.
Good Luck.
 

Similar Topics

I have 3 control panels made by an OEM, they are all identical and have a Siemens S7-1200 PLC with a Siemens CB-1241 Modbus card talking to 2...
Replies
8
Views
4,551
So I have this 2-wire P2000. The total bus cable length is about 200 feet. There are 10 stations, each station with 2 PID controllers. Each PID...
Replies
5
Views
1,691
Hi ! Everybody ! Please..help me about communication between S7 1200 and inverter or any varispeed inverter had MODBUS support by module CM1241...
Replies
20
Views
11,179
I want connect MODBUS RTU device with AB ML1100 PLC to read the holding registers of MODBUS device. In RSLogix 500 I have already configured the...
Replies
13
Views
8,512
I'm trying to understand how the modbus RTU protocol works. From what I understand after reading the Modbus over serial line specification and...
Replies
15
Views
12,082
Back
Top Bottom