Hello,
I have S7-417-4H CPU having Modbus TCP/IP communication with Schneider PLC. Modbus TCP/IP communication was working. But since S7-417-4H powered OFF and ON, from that moment communication is loss. Before power ON-OFF cycle of S7-417-4H CPU communication was ok.
I am using FB909 Block i.e. "MB_REDCL" in OB1 for Communication and same Block used in OB 100 for Initialization. In S7-417-4H CPU rack there is CP443-1 Module used for TCP/IP Communication.
For S7-417-4H CPU 0 port address is 2000 and IP is 172.16.107.0. For S7-417-4H CPU 1 port address is 2000 and IP is 172.16.107.1. Port address for Schneider CPU 0 is 502 and for CPU 1 port address is 503.
Error status code of FB909 is AOFF i.e. "Connection is not ready for communication". I have checked physically the Ethernet cable and related connection but found that all connections are ok.
Please find the attachment of screen shot of simatic manager netpro TCP/IP communication fail status.
Please help me to resolve this communication problem..
Thank you danw,
My s7-400 Have two CPU i.e. CPU0 and CPU1 because of redundant configuration.
In netpro of Simatic manager in CPU0 communication properties there is port address 502 for Schneider PLC and in CPU1 communication properties there is port address 502 for Schneider PLC.
Please see the attached confirmation screen shots for your reference.
Should I changed this port address from 503 to 502..??
Thank you danw,
did you solve this issue? I am facing the same problem
Hello gentlemen, Im working on a small project on TIA Portal, about establishing a Modbus TCP connection between my ET200SP plc and a socomec...
328
Hello, Sorry, my knowledge of communication protocol is limited, so thank you in advance for your answer. My question; I want to get 5 values...
867
Good day Programmers I have a RSTi-EP CPE100 Standalone Controller from Emerson as well as a STXMBE001 (MODBUS TCP/IP) as a Modbus communication...
643
Hello, I'm gonna try to make this as clear as possible. For a project, we have 3 Unitronics PLC's controlling each a machine. The company that...
3,424