Modicon 340 ethernet and two analog module's I/O LED are red(error)
ashu2shreya
Mar 2017
Maharashtra
17
Hello!
I am using schnidler PLC M340 and Unity Pro S,My program is running well and no error but I/O LED's on Ethernet and analog input module is red, according to manual reference error is like
1) "Error detected on configured module or CPU channel"
2)Configuration mismatch with the application (module is missing)
I think I have done write configurations thats why PLC get connect.
Please give me suggestions!!
The analog card I/O err leds will be lit if a channel is enabled, configured for 4-20mA and you have no input or an input of less than 4mA. You can disable the unused channel if you don't want the error light up.
The IO led on the processor will also be red if any card has errors. By Ethernet do you mean the onboard Ethernet on the 2020 processor or do you have an NOE or NOC card?
Also configuring channel to 0-20mA and using custom scaling give opportunity to leave channels unwired, but err led won't lid. If channel is needed later there is no need to reconfigure.
m using onboard ethernet 2020 processer
The IO error shown on the CPU will disappear once you resolve each of the individual IO card errors. Lares solution of setting all channels to 0-20mA and doing your own scaling to account for the "4mA" will resolve this.
It is advisable to make alarm of analog channels on program side, especially if you configure channels so that error leds never goes on.
(raise alarm if AI goes below 2-3mA or above 20 mA, raw values on PLC side depends how you configure channels)
Hi, I am having issues finding how to communicate between a Tesys T LTMR27EFM and a Modicon M340. I have set up all of the ethernet settings on...
3,023
Hello, Modicon enthusiasts ! I have a project I've posted about a couple of times([1], [2]) involving a Modicon M340 controller, and was advised...
3,772
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
404
Hey all, I am having an issue concerning the Modicon System Responsible for the operation of our Generator System. (Particularly Dresser-Rand...
2,564
Hello, I'm having a hard time understanding how to get a Modicon M340 to pull a Modbus address from an ABB Totalflow via Ethernet. I set up a port...
1,158