Modicon Momentum Issue

T Gibbs

Member
Join Date
Jun 2012
Location
Morristown, TN
Posts
406
I have a customer who has a Momentum PLC in a machine. There is a soft start that runs a large hydraulic pump, and about 15 solenoid valves that control the machine process. Sometimes the PLC will shut down the motor and start it right back. When this happens all the I/O cards will flash red lights, then go right back to working. It's like the PLC faults out, then resets. We have changed out the processor, connection cables, I/O cards, etc. and nothing works. It happens at random times. Anybody had this kind of issue?
 
Last edited:
do u have access to ladder logic?

. . if so, can u put in temporary logic to see what is causing the output coil to deenergize?
. . I have a hot date with the wife, so might be a bit before I can get back.

bill
 
It's de-energizing because all the I/O cards are faulting out, then coming back. It's not a programming issue, it's something like a loose connection.
The output points are good for 2 amps each. I wonder what happens if one gets overloaded, like maybe a solenoid coil starting to go bad? I'm leaning that direction, but these fire off so quickly that it would be hard to isolate which one does it. I'm considering adding interposing relays on the outputs, but I don't have a lot of space in the panel, and that's a lot of time to spend if that's not the issue.
 
fused outputs etc

. . our outputs are all fused. an overload on one output should not take down the system, it should just blow the fuse.

. . we had one problem with timing, where the air compressor controllers would bail if they did not receive comms from the dcs within a certain amount of time.

. . battery powered strip chart recorders, hardware or software based, can be used to trend supply voltages.

. . if its safe to keep the pump running with the valve positions questionable, u could run that output through a timer that would keep it energized thru short periods.

. . if a power supply is getting hot and tripping for a second, try running a fan on it.

. . the grilled salmon and attendant scotch were delicious.

bill
 
As geofcc suggested put the cpu on different supply.
It can be a short circuit doing this but something should blow in that case.
I suspect it might me a power supply being overloaded or a tansformer being overloaded when all the loads are on at the same time
 

Similar Topics

Hi everyone, I've recently been having trouble with a Modicon Momentum PLC and I would really appreciate some help. I'm restoring an old machine...
Replies
1
Views
1,935
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
Replies
0
Views
86
Hi Guys, Does Modicon M430 and Momentum Controller have In-Built Modbus SLAVE functionality or do I need to add a Modbus card to them? I'm...
Replies
10
Views
3,159
First time with Unity Pro and a new Unity CBU (Central Brocessing Unit??):) Trying to read the RTC but having no luck at all. Can't be that...
Replies
6
Views
2,214
Hey, gentlemens! I have PLC Modicon Momentum 171-CCC-96030 and ModBus registers list. I need connect to this PLC by ModBus TCP and reading...
Replies
7
Views
5,557
Back
Top Bottom