I don't believe there is a standard pre-defined function block for this. You have to roll your own using four function math and hte folowing principle:
For any unit conversion on any PLC you can use four function math with the following, which
asumes integer math:
DataOffset = Data in input register at 4 mA (or zero analog signal of whatever range - for example 0 VDC on a 0-10 VDC transmitter)
DataSPan = Data at 20 mA - Data @ 4 mA
FACTOR = arbitrary factor (multiple of 10) needed to get proper resolution and accuracy
EU = Engineering Units x FACTOR
EUOffset = Engineering Units @ 4 mA x FACTOR
EUSpan = (Engineering Units @ 20 mA - Engineering Units @ 4 mA) x FACTOR
DATA = Actual data reading in input register
EU = ((EUSpan x (DATA - DataOffset))/DataSpan) + EUOffset
ProcessValue = EU / FACTOR
For Example, 0-60 psig from 4-20 mA with resolution of 0.1 psig:
FACTOR = 10
Data @ 4 mA = 6240
Data @ 20 mA = 31208
DataOffset = 6240
DataSpan = 31208 - 6240 = 24968
EUOffset = 0 x 10 = 0
EUSpan = (60 - 0) x 10 = 600
DATA = 18975
EU = ((600 x (18975 - 6240)) / 24968) + 0 = 306
Process Value = 306 / 10 = 30.6 psig
Remeber there are several different languages available for Modicon Quantum.
Modicon 984LL does not have a predefined analog scaling function. Modicon Concept and Unity both have EFBs (elementary function blocks) for scaling. These blocks can be used directly in LD, List, and FB programming and called in ST. Look at SCALING.
Modicon 984 Ladder has a block called the PCFL (Process Control Function Library) which has quite a few functions including an Analog Input function which is a scaling function. It is available in 685E,785E and Quantum processors.
Modicon Analog Scaling Screenshot (PCFL A-IN)
Attached is a Word doc with a screenshot of the network we typically use for analog scaling.
The PCFL A-IN works just fine as long as your analog device gives you linear feedback. If necessary, you can use the PCFL EQN function for non-linear equations.
-Trevor
PLS SEE THE ATTACHMENT AND PLEASE SEE IF CONNECTION IS RIGHT OR NOT? PLS REPLY FAST.:site:
1,801
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
305
Hey all, I do not have the original source code of a Modicon M172 PLC (HVAC PLC). I want to modify some of the code but read you cant upload...
353
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
409
We've got this old Modicon PLC on a Mobile Skid that has developed "Comm" errors that cannot be cleared (tried moving cables, connectors etc.)...
1,093