Sorry if this has been beat to death.
I have an old Samsung SPC-10 that I want to use for a gate control.
When a momentary push-button contact is made I need it to engage relay 1(Gate Close)push the button again and
it switches to relay 2(Gate Open)
I have the time delays and limits switches worked out.
I have looked at and tried several flip/flop diagrams and can not get them to work, only half works or the relays buzz(scan problem?)
Got this from a diagram, out R015.02 only holds if the NO button(R000.01) is held in
as far as I can find the PLC does not support one shot or DIFU / KEEP
Trigger", "Hold", and "One-Shot" are names I assigned. It is left up to you to choose appropriate addresses for them. For example, "Trigger" might be the real world input address for your pushbutton. The addresses assigned to "Hold" and "One-Shot" can be any available internal (M) addresses or bits of R words.
Edit
Sorry about the reference to M addresses. I don't know the Samsung addressing scheme so I'm not sure if they even have a separate range of discrete nternals or whether you always use bits of R words.
Edit
Ok it does have M and K
Internal Relay (non-retentive) MOO000-MO3115
Keep Relay (retentive) KOOOOO-KO1515
This is also know as a Cutler Hammer D50
same results R015.03 is not holding after the button is released
I would expect R015.03 to be momentary. Or is the above comment a typo?
Any chance of contact bounce? Can you "force" bits? And then test your flip flop with a forced bit as the input?
If all else fails have you tried using a counter, and using the least significant bit of the accumulated count as off or on?
(P) is Siemen's S7 PLC rising edge(oneshot)instruction.
M1.2 stores the state.
Network 2 is basically exclusive Or logic which will toggle the output state (m1.0) each time the button is pressed (I0.0)
We have a compact logix L32E running RsLogix 5000 v.20, connected to two panelview plus 6 1000 over ethernet. 1) One, possibly both panelviews...
2,956
I have created a Vijeo Citect 2015 project with code to mimic a momentary pushbutton. The code sets a Start bit with the mouse button is clicked...
3,182
I am wondering if anyone makes a miniature snap-action pushbutton which looks like a typical 8 mm prox, with a 3-pin M8 connector on one end...
1,773
What is a "clean" way to program a momentary pushbutton so that when pushed the first time it will turn on and hold an output and when pushed...
5,059
See atcched pic. Help me to get it working. Normally the green light will be blinking with one sec delay. When you press a Pushbutton (X2) it...
4,274