using a G120 sinamics i used the Profidrive in order to control the position
in the picture i showed how my system is ,alos how i set the mechanics parameters in the Technologie object,but when Comissioning i don't get a good result for the positioning.
am i wrong !!!
If your drawing is accurate, then your ratios don't match. 117mm would yield 78.4, not 78.5. You're accumulating .1mm of error per revolution.
Where is the encoder for the servo mounted? Motor or Load? If you're getting 23mm movement for a 100mm command, your gearing configuration is not correct.
23 mm movement for a 100 mm command sounds like a combination of quadrature configuration and the arithmetic errors that robertmee pointed out. If you're using an A quad B encoder you're getting 4000 lines per revolution, not 1000.
Neither 37.3 mm nor 25 mm represent an integer number of teeth for appears to be an 8mm pitch. To get the most accurate ratio, instead of measuring the diameter of the pulleys, count the teeth and multiply by the pitch to get the distance traveled per revolution.
I'm with steve. Correct the gear ratio as I pointed out earlier, and set your encoder counts to 4x
i don't have an explanation to this but under basic parameters /encoder i changed A/B count fourfold to A/B count then t works well
i returned to A/B fourfold also worked well
For a system like this where I presume it's just for testing/learning how to set up the software.
I'd ask to move x mm, measure what it actually moved. Then just calculate backwards.
many of the TO parameters have 3 different places the value is stored: in the offline project, in the start value of the TO DB in the PLC, and the actual value in the PLC. If you don't take this into account as you do testing, you can very easily get situations where you make changes that have no effect now, but maybe do later on.
I could very easily see that explaining what you said above, where it didn't work, and then it did work, but then it kept working once you changed the setting back. Something to keep in mind.
I have always controlled servos in Rockwell motion using position loop. I have an application where one process will push against a servo...
274
How do I adjust motion control parameters using Logix Designer? Such as: motion axis stop I will make an adjustment like changing the...
322
Hey guys, On my system, i got prop valve controling cylinder on the left and right to adjust the center of a lumber before it get in a woodmill...
933
Hi, I have an application that currently utilizes SEW drives and programming that we are attempting to convert to Allen Bradley CompactLogix and...
1,147
Hello. We have a Powerflex 700s phase II firmware 4.002, but the encoder card is burned. We want to disable it to use the Drive without motion...
456