Motor Fla

equal yes but not like that. if the label says 30A, then it is 30A per phase. what is the motor voltage and HP rating?

P=1.73*U*I*cos(phi)

P=power
U=voltage
I=current
1.73=sqrt(3)
cos(phi) efficiency (U/I angle)
 
Last edited:
At full load on the motor shaft, expect to find very close to 19.4 amps in each of the three motor phase leads. The motor shaft speed will be close to 1760rpm

Just as a point of interest, at no load, the shaft speed will rise to very close to 1800rpm and the current in each motor lead will drop to around 6 amps.
 
And as an example as to why you wouldn’t consider FLA as the sum of the current in each phase; consider plc_noob’s motor running at full load.

Take a clamp-on current meter and clamp one conductor. You should read 19.4 amps.
Now put the clamp around two conductors. The meter will show? 19.4 amps.
Clamp all three conductors, and now the meter reads? 0 amps.
 
Why would you get a reading of 0 amps with all 3 phases clamped?

Kirchoff's Law:
At every node, the sum of all currents entering a node must equal zero.

ii1=0 (1)
i1i2=0 (2)
i+i2=0 (3)

When you clamp all 3 leads then it must equal zero because you are looking at the sum of all the currents at the same time.

Here is a good web page that explains this:

http://cnx.org/content/m0015/latest/
 
Last edited:

Similar Topics

Can someone please explain how the FLA in the attached table came to be 14 AMPS instead of.... (1000*0.75kW)/(1Pf * 115vac) = 6.5AMPS...
Replies
16
Views
5,133
Hi. This is not a PLC-related question, however, I know there are a lot of experienced practitioners on this site. I really need to ask this. I...
Replies
22
Views
4,772
Because of 3 or 4 posts with errors on this subject, this US National Electrical Code admonition needs repeating: NEC Handbook Article 430.22...
Replies
10
Views
5,858
Hope you are doing well. Currently, I am involed in a revamping project. It requires to stop a mixer at specific postion. For the detail, this...
Replies
3
Views
80
I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
Replies
9
Views
228
Back
Top Bottom