MP377 Logoff Times

Michael Hunt

Member
Join Date
Nov 2008
Location
Leeds
Posts
75
Hi

I have a SIMATIC MP377 HMI. All my users log off automatically after 5 minutes.

My question is where is this 5 minutes set. I currently have to go into every user and change this manually. Is it possible to change the default from 5 minutes on the MP377 or using WinCC.

I would like a logoff time of 30 minutes for each user.
 
the time is set in wincc flexible under
runtime useradministration:users (logoff time) or if you have an admin screen on the panel it can be changed on that if the option was enabled in wincc flexible
i think max is 60 mins
regards
Mel
 