MSG communication interuption
Darkzadow
Nov 2011
Phily
94
I am testing communication between 2 rslogix 5000 PLC's one is a inuse system on the plant and one is a test system that will be put inuse later. The inuse system has a laser gauge connected to it. I used a msg instruction (CIP data read) to try to bring this value into the test PLC it worked the first time. Now the laser gauge no longer updates its values. I see on the hardwired gauge it reads correctly but PLC no longer updates the value.
My question is, can a CIP data type read, interupt communication on PLC it reads from?
My first question would be are you seeing the value change in the PLC that you are reading from?
If so when you are reading the value from the 2nd PLC what instruction have you got in front of the MSG instruction?
Can you show us a screen shot of the message instruction and how it is set up?
Mark
I found the problem. I did see the value change. Unknown to me the electricians turned the plc off so comm between PLC and lasers was never reset. Which I found out after the operators turned lasers on and off resetting connection.
Hello all, I am currently trying to establish a message instruction to pass data from a 1756-L73 to a 1756-L71. My communication path from the...
377
I am re-writing a mess the last guy left me. And a question came up on MSG execution logic. So this code is Reading and Writing to a MicroLogix...
1,814
Hello, I am using a Compactlogix 5380 PLC and need to read values from a few existing PLC 5s, other Compactlogix PLCss, and a few Controllogix...
4,381
I'll start off by saying I'm unfamiliar with communications between PLC's, hence my question here. We have a machine with a ControlLogix & a SLC...
2,796
I am trying to communicate with a Moxa Ethernet to serial converter that is going out to a Modbus device. I have my Moxa set up with an IP of...
2,921