Micrologix1400 MSG Error: Local Communication Channel is Shutdown
jolson148
Mar 2019
Wyoming
I am trying to communicate with a Moxa Ethernet to serial converter that is going out to a Modbus device. I have my Moxa set up with an IP of 192.168.1.98 port 4001. I have my MSG instruction set up as
1(integral, Modbus TCP)
03 Read holding registers
trying to poll 1 element @16bit
I have a valid RI11:0 entered
IP of 192.168.1.98 and port 4001
I keep getting a fault code ff and the description is local communication channel is shutdown. I have Modbus tcp enabled under channel 1 configuration and have the channel 1 Modbus tab at the top.
What am I missing or doing wrong?
Welcome to the PLCTalk Forum community !
Why are you using TCP Port 4001 instead of the standard Modbus/TCP Port 502 ?
Also, be sure you have power cycled at least once after Enabling Modbus/TCP on Channel 1. That function requires a hard reboot at least once after it is enabled, and the FFh error code is characteristic of that issue.
Glad to hear you got it sorted out, and I appreciate the response post.
I recommend that you configure the Moxa and the MicroLogix to use the ordinary "well known" TCP Port 502 for Modbus/TCP.
Port 4001 is a "registered port" with unofficial uses, none of which are relevant to Moxa or Modbus/TCP (like the old Microsoft Ants game !). If somebody had to come analyze your network in the future they would start looking for Port 502.
Hello, Is it possible to msg write 1 bit from micrologix 1400 to micro820 over ethernet? I'm an electricain with only knowledge of 500CPU and...
2,317
Hello, Well I'm back to my project that many of you have helped me with. The plc that I have is a ML1400. My goal was to message some data from a...
4,255
Hi All I have a Panelview 800 HMI hooked up to a Micrologix 1400 controller. I have communication and have the screen set up with some...
934
I have tried to find this everywhere and I am really not sure what I am doing wrong. I am trying to use a CompactLogix and the message functions...
2,791
Hi Friends, I am trying to connect MLX1400 over RS232 serial communication with PV800. I am not sure where I am going wrong, the PV800 doesn't...
958