PV800 to Micrologix1400

14sherman

Member
Join Date
Aug 2022
Location
Belleville
Posts
2
Hi All
I have a Panelview 800 HMI hooked up to a Micrologix 1400 controller. I have communication and have the screen set up with some pushbuttons, a numeric displays and a numeric entry. Everything works except I can't get the numeric entry to write to an integer file in the PLC. It comes up with a write error. I think I have the tag set up correctly since it will read it. Has anyone had this issue? I've searched here with no luck. Thanks
 
Looks like I got it fixed. Downloaded the program to the 1400 again and cycled power to PLC and HMI as per an AB knowledgebase article and it worked.
 