30 seconds is the standard CIP Connection timeout.
It really, truly, genuinely sounds like an honest-to-goodness IP addressing problem.
Are you certain that the two devices are on the same IP subnet ? Post the actual IP address and Subnet Mask of both the 1756-ENBT and the 1761-NET-ENI.
To do anything else you're going to need a mirror port or remote capture of the Ethernet traffic.
One more thing: The 1761-NET-ENI tool, for some reason, requires you use leading zeroes in the fields in which you place the octets of the IP address. It always interprets these as decimal values.
In any other notation, including the Windows command line and the CIP path field in RSLogix 5000, a leading zero in an IP address octet denotes that it's an Octal number, not a Decimal number and 80 is an invalid number in Octal.
Your postings show that the last octet is entered in RSLogix 5000 as "80" but I wanted to cover this little detail. It has always irritated me that the Net-ENI utility forces you to use an incorrect notation.
Problem fixed. The compact logix did not have the gateway address listed in it's processor port configuration for TCP/IP. Even though the network VPN could communicate, the PLC did not konw how to leave the network to cross over to the secondary side. Oversight but costly in time.
LocalENB, 2, 192.168.126.80 was the proper path syntax.
Gateway is not an issue if all devices are on the same network as a lot of systems are. PLC was setup over a year ago and this information was left out, probably because the PLC was setup offsite.
Lesson learned!
i know this is a old thread but i am having the same issue. i tried to download the telnet tool but it appears to not be working on my computer. i am online with both devices currently. could that be taking up too many cip connections and causing the message to fail?
hi , I need to sorry for my bad English first. I'm newbie at plc programming ,I had been asked about E/IP protocol information for some system...
389
Im trying to use a MSG instruction to get the serial numbers of all addon cards and display the serials on a HMI interface. I have the logic done...
566
Is it possible to configure the MSG instruction in CompactLogix to communicate with another CompactLogix in online mode or should the PLC be in...
1,399
So I have been on site this week doing integrations, and issue came up where I need to talk to an old PLC5. I tried using the path I usually...
2,589
I have two 1769-L32E Compact Logix PLC controllers. One the remote plc I have two msg instructions setup to read two separate ESD tags from the...
4,543