Easiest way to combine all data on the PLC5 in one file and send it in one message.
If multiple messages used, each one must have own control.
Use .DN bit from one message to start another one, don't send them all at the same time.
If multiple messages used, each one must have own control.
Use .DN bit from one message to start another one, don't send them all at the same time.