Hello,
We have a local push button station going to a PLC in a safe area. There is a 7 core cable connecting the station to the plc.

Core 1 24v
Core 2 spare
Core 3 push button 1
Core 4 push button 2
Core 5 spare
Core 6 spare
Core 7 earth

My question is why is core 7 an earth cable, can’t think what I’m missing? Is this to stop induced voltages on the other cores?

Thanks

Thank you
 
Any box, door, container ... that has an electrical device, even a simple 24V pushbutton, must be grounded and this cable seems to be used for that.
 
You have not stated what type of multicore it is but if the cores are numbered with 1 unnumbered green and yellow cable then the cable is probably either LIYCY or YY.
The standard core colouring for these cables is for 2 black cores with white numbers for 2 core cable, and for 3 cores and above it has black cores with white numbers all except 1 green yellow.
It is the standard construction for these cables. Depending on what it is used for, you may or may not need the Earth, but if you do it is there and clearly identified.
 
Thanks for this. The box also has an earth cable connected to nearby steelwork. I was just wondering why use both?


Thanks
 
Does the earth core go to an earth terminal, either on the box or on the terminal rail?

If so, then you are connecting from the cable to the box to the steelwork, to prevent any cable fault giving a voltage on the earth core, and potentially you, the user, touching a potential from the box.
 

Similar Topics

Hi, Can I have genius thoughts on if there will be any concern if I run RS-485 2-wire cable with Analog input in one multicore cable lets say...
Replies
6
Views
3,529
Hello, I'm currently in Houston, Texas, and going on a job in Louisiana next week. We had some supply problems over from Europe on the TC cable...
Replies
5
Views
2,046
I’m working on getting a Parallel Redundancy Protocol PRP system set up in a lab situation. The L73 PLC is in rack 4. 3 io racks are 1,2,3. I...
Replies
6
Views
755
Hi all. I'm having a hard time figuring out which cable goes with which module from Rockwell documentation, and my local Rockwell representative...
Replies
4
Views
836
Hi, The distance between a Yaskawa VFD GA700, 45KW and the motor is 75 meters. I am using an output inductor between the VFD and the motor. I...
Replies
2
Views
943
Back
Top Bottom