Cabling between VFD and motor
2rlp
Sep 2006
Mumbai
136
The distance between a Yaskawa VFD GA700, 45KW and the motor is 75 meters. I am using an output inductor between the VFD and the motor. I would like to know of the following options, which would be better to use
Option A: A 35sqmm 3 core cable,
or
Option B: 35 sqmm 3 separate flexible wires, laid in a conduit pipe
Ron
Manual shows screened cable but no inductor - contact the drive tech support and ask for their recommendation, you dont want to have to do it again with 75m of cable.