Need Help on programming
dani90
Apr 2012
Canada
39
Hello Experts,
please help me out on programming.
inputs
tank full float switch
tank empty float switch
outputs
inlet solenoid
drain solenoid
mixing pump
Sequence starts with start button.
empty the tank
fill the tank
run mixing pump for 10 minutes
drain again
stop the sequence.
Try writing it out... then make your program
1) close solenoid and fill tank
2) fill tank until float is reached
3) turn on mixer for 10 min
4) bla bla bla
Then after your sequence is wrote convert that into ladder logic
Try thinking of it as a series of 5 steps.
Step 1 is waiting for the start button.
Step 2 is draining the tank.
Step 3 is filling the tank.
Step 4 is mixing.
Step 5 is draining.
The system must always be in one of the steps, but it can't be in more than one at the same time.
Which outputs are on at each step?
What conditions must be true to make the transition from one step to the next?
Program Question
@jtteresinski I like your code a lot. If I may ask, how come you use binary outputs instead of actual outputs on your initial rungs? I've noticed many programs at my plant are also set up like this, having one ladder with binary outputs, then a second ladder with the physical outputs.
Thanks.
I dont want to answer for jtteresinski (I agree nicely written) , but I do the same... for several reasons
1) outputs for me should be last as you can have several conditions of the scan affect the condition of the logic
2) large programs I know where to find my outputs and really large will have their own sub-routine
3) keeps it cleaner, I can have several rungs that will latch and unlatch a bit but the work is done at the end
4) small programs I write the known's inputs, outputs, timers, counters, etc then fill in the blanks
Thanks for compliments.
The main reason, as @geniusintraing stated first, is that I learned, both through trial and error and then instruction, outputs last! It is likely you will have more than one condition to turn on an output...so if you turn it on in rung 5 and then realize later in the logic you need it on again because of a reset sequence...things can get confusing..both for you and anyone that needs to get into the code later.
I was brought up in the SLC500 world when I learned programming and if you had the same output in 2 or more places in a program, then only the last one worked. The newer stuff (contrologix, etc.) can maybe do this?
I've programmed a fair # of machines using this type of "step" method...it's made sense to my simple mind and I've found it easy to navigate and find where/why machine is stuck as have maintenance personnel that I have reviewed it with.
I don't think there is one right way...every machine is different as is every programmer. Find what makes sense for you.
Where I am know I am a Machine Tester...verify custom equipment meets customer specs., debug, find issues (mechanical, electrical, program) and the controls group here programs in State Logic (if step done, then move 10 to state, if = 10 then do something, when done move 20 and so on)...I hate it! Though it really isn't that different than what I am doing.
I am very much a newbie to programming. I think I have done it a completely different way. I’m happy to take comments/criticism.
This is close, but I think the drain step will only happen 1x (after the mix is done), the way I read it?
The sequence was drain, fill, mix, drain.
Thank you for the feedback. I thought that it would automatically drain again ?
Hello there, I'm practically new to the PLC world, I'm quite familiar with Siemens TIA Portal but I'm currently tasked to program Schneider PLCs...
1,863
Hello, I’m currently working on a project using a unitronics samba plc, I need to create a program with a touchscreen start and stop button, that...
2,274
Hello i need one of you fine gentlemen to help me with some ladder logic. I'm brand new to PLC's and admire you guys, i'm a long time stalker...
5,088
I work for a small town company and we have been growing, they recently bought a few Panasonic performarc robotics that have manually operated...
1,421
Dear sir. i have one Automation Direct hmi, if you have the CMORE Programming software,i will send you .eap file in email, can you please...
2,442