Hi Guys, i need help setting up a analogue speed input on a fr-e540-2.2k-ec inverter, at the momment we control the speed manualy but now we need our plc/remote i/o (1734 allen bradley) to control the speed, i have an analogue module set up which it is 0-10v i have connected analog to 2+ 5 on the inverter but i am not to sure how much i me to change in the inverter settings?? i think pr79 needs to be 0 & pr73= 0? can anyone help?
I'm not an expert and I don't have the E series manual but I think you may need to adjust Parameter 903 as well.
Be sure RH, RM, and RL are off or they will override your signal.
Steve.
hi dave
i took your advice and replaced it with a powerflex 40 and all working, thanks for your time. stu
To Dave
I tend to agree with you, the 500 series are obsolete now, but check out the new A700 series, they are powerful, and i have to give them this, they are very user friendly.🍻
Similar Topics
I am working on setting up my own 1756 B series PLC rack, power supply 1756-PB75 /B, 1606-XLS480E -redundant 24 DC power supply, controller...
Replies
6
Views
4,324
Hi everyone! First time posting to this, so should give you a bit of background info on myself to explain the situation i'm in. I am a beginner...
Replies
4
Views
1,585
I am new to compactlogix 1769 L30ERM PLC. when I was upgrading firmware to version 30 through control flash flowing error came. it is; and also...
Replies
6
Views
3,046
Good morning, I was wondering if anyone was familiar with the process of setting up an EGD exchange from a robot controller to a PLC. The PLC is...
Replies
3
Views
2,784
need help setting up a jar filling machine...HELP!! i need help creating a logic control that can process this requirement. I have extremely...
Replies
9
Views
2,290
Back
Top Bottom