Need Help With Input Card on GE Fanuc Series 90-30

how do i upload a program to the 90-30 using LM90 from the laptop
Be careful of your terminology and what it means. From the way you worded your question I come to the conclusion that to you, "Load" means a data transfer from the PC to the PLC. That is exactly the opposite of what Logicmaster means by "Load". That misunderstanding is probably what got you into trouble in the first place.

Pay close attention to what Logicmaster tells you about the direction of the data transfer. Only hit the "Y" key when you are sure that you understand what is going to happen when you do.

Be sure you are clear about which Logicmaster sub-menu you are working in. In the "Load/Store/Verify" menu you are transferring data to and from the PLC. In the "Folders" menu you are dealing with the project file.
 
I don't mean to re-drag this post up but I wanted to let everyone involved know that it was in the field wiring. It was a loose wire on the power supply causing the cards to drop out and not show any input changes or output changes. Thanks for all the help guys and for putting up with me.
 

Similar Topics

Hi, I am pretty good with Rockwell gear but I am fairly green when it comes to Siemens and I am having difficulty finding where an analog ASi...
Replies
11
Views
3,979
Hi, I have a Micrologix 1400 with a 1762-IQ16 discrete input module, wired for sinking inputs (common to DC-) I have an instrument with the...
Replies
5
Views
12,724
hello... i'm trying to take an analog value from transmitter.. i'm using OMRON CS1G-CPU45, and the analog module is CS1W-AD16, the analog value is...
Replies
1
Views
1,449
I've got a AB PICO 1760-L18AWA, it accepts 120V input. I've got a circuit going thru a 120V solid state relay (SSR)that is activated by Thermo...
Replies
7
Views
2,859
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
47
Back
Top Bottom