Node numbers for Controllogix redundancy
duncan
Jan 2005
17
Hello Friends,
I have a redundant 1756-L55 pair.The two CPUs are in two corresponding Chasis.These are connected to two more chasis on controlnet for Remote I/Os.
For all these 4 chasis what are the node numbers?
Is there a common node number for both CPUs in adjacent chasis for redundancy?
Thanks.
Duncan
Hey Duncan, did you read the manual for the ControlLogix Redundancy System?
Anyway, you must address the I/O chassis CNBs with node no. 1 and 2. The CPU CNBs will have address 3 and 4.
I suggest you to read the manual. It's well written and gives you various suggestions in order to optimize your system and avoid problems.
I have a controllogix redundant system in service, and here is my controlnet addressing:
Primary Chassis (Chassis A) - node 10
Secondary Chassis (Chassis B) - node 11
I/O chassis has 2 CNB's - nodes 1 and 2
I use node 1 for RIO comms and node 2 for ENBT comms. This way, if there was a failure, I would immediately know where the problem was.
There was some disscussion around putting all comms on one card, but since we have spares readily accessable and within short distance, the risk was minimal.
Regarding the processor nodes - the SRM module will switch the address to the primary node number upon switchover. Thus the primary chassis is always node 10.
Hi, I have established a connection through rslinx. When i try to configure the DH-1 driver with a node address by going to system options &...
31
10,819
Dear all, I am beginer in ifix hmi programming. I have 2 ifix 6.0 pc with license FiX and client.. Can some one tell me how to configure sample...
162
Looking to tery and send some tags from wincc to node red dont have a wincc connectivity license so can use opc. Any suggestions ?
79
Hello All, getting my feet wet currently with Node-red, curious if anyone has experience with the SMB share add-in(or whatever the terminology...
305
Well actually I'm a person and not a fan but either way. I'm an old in-my-60's PLC guy and I recently had a project which spec'ed for a...
1,227