NOISE ON 4-20ma
KEN_KACEL
Nov 2002
NORTH COUNTRY
162
The Phase 2 of our project uses deviceNet IF4I analog input cards. The devices hooked to the input cards are Pressure transducers. When the device(PT) is grounded to the building ground the inputs goes to 11ma when disconnected it will go to the normal 6ma. This value is affected by the 100HP vfd in the cabinet. We have searched high and low for wiring problems and also added 1746I8n to the main rack and still get the rereferenced signal. The potential between the PT device and ground is 20-40mv.
At our wits end !!!!!!
It isn't clear why you would ground the pressure transmitter.
What you are seeing is a classic ground loop.
Please show us the wiring, including the power supply; and include model & brand of the pressure transmitter.
The sensor should be grounded as it can be touched, however the signal ground should only be grounded at the cabinet.
in many sensors the - of the supply is grounded. so this way you will need a separator in between.
what is voltage between machine and cabinet ground.
Is the ground cable from motor big enough?
is cable shielded?
Hello, I'm working with a PLC reading a basic 4-20mA 0-100 PSI water pressure sensor which is used to measure an elevated water tower tank level...
17
9,449
I'm really stumped on this one. I have a Turck linear transducer connected to a 1762-IF4 analog module on a MicroLogix 1400, configured for...
22
6,909
Long story short, I am building an electrical panel at work that involves roughly 20 Allen-Bradley PowerFlex 4 VFDs. All VFDs run on 480 volts...
7,624
Hello, I am running a AMCI SD4840 Stepper Motor drive system with Allen Bradley CompactLogix. Every now and then when a 480VAC motor kicks in on...
592
Hello Everyone, I hope we are all well. I have an L36ERM with a 1769-OF8C/a driving a 5HP Power Flex 523 speed reference 4-20 mA. With the...
1,839