nt600s trouble

ahmed yousri

Member
Join Date
May 2006
Location
egypt
Posts
41
There is message appeared at our touch panel"NT6005" which cause of production line stop. This message is "NAK Received (end code simultaneously displayed)"

And this trouble occurred only in first production line. And the other production lines were not affected. Please mention the reason of message, and how can we avoid it at the future?
 
I guess you mean NT600S. I do not know the message. There are Omron gurus who come here. One of them may be able to assist with the message.

I fail to see how a screen problem can stop the PLC. Do you mean you cannot access the touch screen or the PLC stopped?

By the way, you should mention brands, models etc or no one will know what you are referring to.
 
Manual #V022-E3-1, page 246 indicates the error comes from noise in the cable while receiving data.
 
I already read the manual , but the strange thing ,this trouble occurred only at the first production line and did not occur at the other lines ,all production lines feed with one bus bar feeder
 

Similar Topics

Dear Sir/Madam, There is a sitution with a Omron PT NT600S-ST121-EV3. When started it goes directly in program ,when it is disconnected from PLC...
Replies
1
Views
1,542
Hi i'm new here and i'm not even sure if i'm in the right place. At work i've been asked to see if i can fix the screen jn one of the roto molding...
Replies
4
Views
2,351
Welcome everybody I get used nt600s but i have communication problem NT-series SUPPORT TOOL ver 4.82 between NT600S-ST121-EV3 I read all post on...
Replies
7
Views
2,815
Hi ! I have a Omron CQM1 CPU43 PLC and Omron NT600S touch display. Occasionally (too often) the NT600S goes suddenly to "connecting host"-mode...
Replies
1
Views
4,156
Hello All. I have no experience with Omron PLC and I am asked to find the problem in the working system. I have: PLC – SYSMAC CQ1 CPU45-V1...
Replies
6
Views
6,618
Back
Top Bottom