Old PanelView Plus files....

daba

Lifetime Supporting Member
Join Date
Jul 2004
Location
uk
Posts
5,401
.... I have View Studio version 6, and some application runtimes (.mer) written in version 4.

View Studio can't re-create the application files... It says version 4 didn't support that feature.

Does anyone know of a possible work-around, I don't think the source files are obtainable.
 
daba said:
View Studio can't re-create the application files... It says version 4 didn't support that feature.

That's correct daba. You can only create MER files at Revision 4, no option to restore the project.
The restore to design time option, when creating runtime files, wasn't added until FTVS Revision 5.00 and above.

The tech note that I think Alan is referring to is here 8913.

Note: The work around does not completely restore the project.
Some aspects such as...

Parameter files
Alarm Setup
Datalog files
Macro files

and in some cases, the Tag Database, will not be restored.

Attached is a PDF of the step-by-step for the work around.

G.
 
Thanks for that, Geospark, it confirms that I will not be able to achieve this with the licensing I have, as I would need the >5 display runtime license, and it looks like I would need version 4 (not 6, which I have) to "recover" a version 4 .mer file.

I only need to assimilate the actual animations performed by the PanelView displays in response to the numbers sent by the PLC, not interested in alarms, parameters, etc.

If anyone has the necessary licensing for Version 4, and is willing to "have a go" at recovery, PM me and I can send the .mer file (there are 3 installations, but I know from the PLC code that they all work the same way).
 

Similar Topics

Hello . Info: Panelview plus 400 2711P-K4M20D Compactlogix 1769-l32E i make a program in RSlogix 5000 and Factorytalk view for...
Replies
9
Views
1,822
Hi All! Is it possible to establish any remote access on PanelView Plus 2711P-T10C4D6 (logic module 2711P-RP6)? This panel is running WinCE 4.10...
Replies
3
Views
1,871
Good Afternoon , I have 3 old Panelview Terminals that I need to replaced. Could you tell me the replacement for the Panelview Terminal 600...
Replies
4
Views
1,893
Good Morning , I have several Panelview Plus 700's off of old machines. I would love to use these for small machine upgrades around the...
Replies
5
Views
2,306
Hi all, I'm starting a project where I have to convert an old HMI to work on a new panelview plus 7. A person who used to work for us, but does...
Replies
8
Views
2,859
Back
Top Bottom