yazan83 Member Y Join Date Oct 2007 Location Damascus Posts 20 Oct 29, 2007 #1 on omron c-series instruction set how can i use rising edge with set and reset instruction . ?
yazan83 Member OP Y Join Date Oct 2007 Location Damascus Posts 20 Oct 29, 2007 #2 where are the people , please i need help... Last edited: Oct 29, 2007
bluebyu Member B Join Date Aug 2005 Location Pa Posts 263 Oct 29, 2007 #3 What is the PLC model? What method do you have to program the PLC with? Do you have the manual?
Paulus Member P Join Date May 2004 Location Portsmouth Posts 416 Oct 29, 2007 #4 Hello Yazan83, As bluebyu states, what device are you using? Help us to help you! However, I believe that you cannot use differentiation on a SET instruction for C Series, nor diff-up the contact before it.
Hello Yazan83, As bluebyu states, what device are you using? Help us to help you! However, I believe that you cannot use differentiation on a SET instruction for C Series, nor diff-up the contact before it.
mordred Member Join Date Mar 2004 Location Red Deer Posts 1,892 Oct 29, 2007 #5 use @set and @rset double check your processor model and the instruction set for whichever processor your using hopefully the model your using supports the variations the one you want is set differentiation upward
use @set and @rset double check your processor model and the instruction set for whichever processor your using hopefully the model your using supports the variations the one you want is set differentiation upward
Paulus Member P Join Date May 2004 Location Portsmouth Posts 416 Oct 29, 2007 #6 Hello Yazan83, Done a bit more research for you... You need to use the DIFU (or DIFD) instruction... I.e. LD 0.01 DIFU(13) 0.02 AND 0.02 SET 0.03 or Mordred, fairly sure the "@" cannot be used with C Series (C200, C200HX, CQM1, CPM etc) SET / RSET instructions. Hope this helps
Hello Yazan83, Done a bit more research for you... You need to use the DIFU (or DIFD) instruction... I.e. LD 0.01 DIFU(13) 0.02 AND 0.02 SET 0.03 or Mordred, fairly sure the "@" cannot be used with C Series (C200, C200HX, CQM1, CPM etc) SET / RSET instructions. Hope this helps
mordred Member Join Date Mar 2004 Location Red Deer Posts 1,892 Oct 29, 2007 #7 yeah I wasn't sure on that and I didn't have that series of programming manuals handy