Omron C200HX and DA004 gives 0x00D0 error - Duplex / Special IO unit error

stanleykapo

Member
Join Date
Jun 2015
Location
Kosice
Posts
1
Hello,

I have a problem with installing Omron DA004 card in the C200HX PLC. In CxProgammer it keeps giving me "Duplex / Special IO Unit error" on the processor. This is non-fatal error and the PLC keeps running, but analog outputs on this card do not work.
I tried putting it in different slots and racks, but this still does not help. I am quite sure that I have done the IR and DM setup correctly, and I had this checked by Omron Support specialist in Czech Republic.
The trick is, I am very much sure the problem is not with the card. I took this card and put it in a different PLC and it works without any problems. I also took working card from the different PLC and installed it in my original PLC - and the error keeps appearing.

Does someone have any idea on what else I could try?
 
You had this error logged elsewhere - no result? Have you tried placing the problem at Myomron? Really weird - have never had a problem with these. Have you checked to see that the address on the card does not clash with the address on another card? http://www.myomron.com/ You have to join but it is free. I wonder if it could be a version number mismatch - what is the other PLC where you have tried the card?
 
Check the Unit # setting on the rotary switch on the front of the module. Also check any other modules with a Unit # switch.

Each module requires a different Unit number.

Not sure this is the issue, but would be the first thing I would check.

Hope this helps.
 

Similar Topics

I can't figure out how CX-Programmer is connecting to this PLC. - C200HX PLC - in the field. - Laptop connected to a network via ethernet cable -...
Replies
3
Views
2,479
Hi..any expert can advise. I have a old or not very old Omron C200Hx-CPU85z series which I plan to upgrade. I know CS1 series is the recommended...
Replies
1
Views
2,319
Hi guys, do you know if Omron Sysmac C200HX peripheral port supports the FINS serial protocol? Thank you Regards Mike
Replies
3
Views
3,196
Hi guys, I have the following setup Omron Sysmac C200HX connected to a HMI panel using serial port. I need to access some data in the PLC...
Replies
12
Views
8,565
Hi, I have an Omron C200HX connected to Citect. Recently there's a problem with specific data point. The data is received at Citect but at...
Replies
3
Views
2,772
Back
Top Bottom