Omron Encoder
hello
in absolute encoder 8 bit - 256 states per revolution
0 = 0 degree
255 = 359 degree
resolution 1,40625 degrees
regards
He was noting that 1/256 of 360 degrees was 1.40625 degrees (the comma being a common alternate to the decimal point). Thus the degree resolution of one increment of this encoder.
Thanks again for the replies.
Please refer to attachment and answer these question:
1- Is it true that in one revolution (o to 360 degrees ) bits 2 to the power of 0 to 7 are generated ?
2- what the address indicate at the bottom of the page?
From the timing diagram it appear that this encoder presents the data in Gray Code. If you aren't sure what that is please check here
Also check your PLC for any Gray Code conversion instructions.
Another note - the ouptu shows as NPN. Ensure you have the correct polarity on your input module.
I know you haven't actually said anything about a PLC but since this is a PLC site...
yes Output is in 8 bit Gray code.
Below image with difference in absolute encoder outputs.
next :
at the bottom of your document is decimal value of encoder position
Converting from Gray to binary is simply :
Sample for 4 bits
Gray Bit0 - M0.0 ( or input %I0.0 )
Gray Bit1 - M0.1 ( or input %I0.1 )
Gray Bit2 - M0.2 ( or input %I0.2 )
Gray Bit3 - M0.3 ( or input %I0.3 )
binary BIT0 - M1.0
binary BIT1 - M1.1
binary BIT2 - M1.2
binary BIT3 - M1.3
Program in IL ( Instruction List )
LD M0.3
ST M1.3
LD M1.3
XOR M0.2
ST M1.2
LD M1.2
XOR M0.1
ST M1.1
LD M1.1
XOR M0.0
ST M1.0
best regards:p
HI
At the moment I am not concerned about programming just trying to explore this type of encoder Thanks for the input guys
#1 - YES (in grey code for the model you are looking at)
#2 - The address indicated is the rotational position of the encoder.
Unlike incremental encoders who can loose their position on power down, the absolute encoder will pesent its current position on being repowered even if moved.
HI
Please see the attachment and I like to get clarified, my understanding from the attached drawing is that in one complete revolution of the encoder shaft in this case:
(4 bit encoder) only once those gray codes is generated and exact the same thing is repeated in next revolution and so forth.
Thanks a lot
HI BERNIE
Thanking you so much for the reply, I will get back to you for more questions and I hope you do not mind it. thanks
Distance Measurement
HI EVERYONE Regarding 4 bit absolute encoder after conversion from gray to binary code then each output pulses are counted and added together and result is equivalent to distance traveled for example say one meter.Thanks
I am providing 24 volts on encoder input but getting the 24 volts on encoder output.The output voltage is not changing,so I want to ask what will...
2,355
Dear all PLC's master, I'm trying to connect CPM1A to rotary encoder (Omron E6B2) using PRV with this code (0 0 DM100), but i can't read the...
6,174
Hi All, Need some help regarding MicroLogix 1400 HSC, Can I use Omron Encoder : E6B2-CWZ6C 600P/R... I badly need help.. Thank you very...
4,341
hi i am a beginner, can any one help me to use encoder or a proximity counter to calculate the positioning of belts.
16
6,660
Help needed, Is there anyone who ever write code for OMRON Rotary Encoder with MicroChip's PIC16Fxxx series. I'm seriously needed. Thompson Soe...
3,461